Read 690.9(D) and 690.34. Not sure where this "hysteria-run for the border"
sentiment is coming from.
690.9(D) Photovoltaic Source and Output Circuits. Listed PV
overcurrent devices shall be required to provide overcurrent
protection in PV source and output circuits. The overcurrent
devices shall be accessible but shall not be required to
be readily accessible.
690.34 Access to Boxes. Junction, pull, and outlet boxes
located behind modules or panels shall be so installed that
the wiring contained in them can be rendered accessible
directly or by displacement of a module(s) or panel(s) secured
by removable fasteners and connected by a flexible
wiring system.
This is not a change. Please help me understand the concern.
Bill Brooks.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Monday, April 28, 2014 2:23 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] (no subject)
Interesting so does "require a tool" include taking a screw off the cover
plate of the combiner box, too?
What a game changer. I'm going to Mexico for my next project; I'll actually
enjoy even more being the sole AHJ on the project.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/28/2014 2:52 PM, Michael Morningstar wrote:
Readily accessible is now defined in the 2014 NEC. Installing OCPD's
underneath a module is a major faux paux, and I can't imagine any AHJ
thinking otherwise. Having to remove a module in order to reset a breaker,
what a drag.
"Capable of being reached quickly for operation, renewal or inspection
without requiring those concerned to use a tool, to climb over, remove
obstacle or other."
Michael
On Apr 28, 2014, at 10:29 AM, William Miller <william at millersolar.com
<mailto:william at millersolar.com> > wrote:
You call it a solar panel, I call it a glass j-box cover plate.
William
Miller Solar
On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <jason at fafcosolar.com
<mailto:jason at fafcosolar.com> > wrote:
If that is the interpretation,
I don't see how the breakers are "readily accessible" in a SolaDeck
mounted anywhere, regardless of whether it is under a module. It
requires removal of four screws (using a tool) to access the breakers
inside the enclosure. It's all up to the AHJ. It has not been an issue
locally here. I can see how other jurisdictions may not
concur.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140428/d8288b12/attachment-0003.html>
More information about the RE-wrenches
mailing list