Here is exactly what I ordered:

(1) RST0760-41AD Soladeck AC/DC Combiner Box
(1) RST0784AC-3K Soladeck AC 3 Circuit Busbar Kit
(2) RST1455.20 ABB Mini Circuit Breaker 120/240VAC 20A
(1) RST1455.15 ABB Mini Circuit Breaker 120/240VAC 15A
(1) RST1440.080 Soladeck Power Block 600V 80A

​This model has a cover that is bumped out to fit breakers. Here is a pic
of the closed up box.

​[image: Inline image 1]

Again, I'm not really happy with the way I brought the Enphase cables into
this ​Soladeck. The knockout center-points provided by the manufacturer are
too close together to accommodate five water-tight glands, so I used some
offsets to make more space. If it wasn't my own house, I would have wanted
it to look much prettier for a customer.

One thing I highly recommend is along the top and sides to use sealant as
indicated in the manual, then sprinkle a generous amount of granules in the
sealant. Otherwise the cover and your fingers get gummed up when taking the
cover off.

​The manufacturer's website and documentation is woefully inadequate for
this product. They need to clarify it, obviously, based on this discussion
if they want to sell more. It's a great solution IMO.​


Jason Szumlansk​i

Fafco Solar




On Wed, Apr 23, 2014 at 12:01 PM, Chris Schaefer
<chris at solarandwindfx.com>wrote:

> Jason,
>
>             I love the picture. Just ran into this a few days ago on an
> install. Had two older SolarDeck Model 0780 in stock. I had the same two
> pole breakers and attempted to install them here in the shop before I went
> out to the project as I was afraid their height would not allow the cover
> to seal. And it did not. It appears you have ABB breakers and I just tried
> them and they don’t fit either. Now if you look at your link it shows and
> states fuse holders, which do fit. I’m wondering if the newer models in
> your link are just a little bit taller than the older models I had in
> stock. I don’t see size specs on their web site. Can you please provide the
> model# you show in your photo?
>
>
>
> Christopher Schaefer
>
>                                 Chris Schaefer’s
>
> [image: SolarWindFX]
>
> *                    Tel/Fax 585-229-2083 <585-229-2083> or Cell
> 585-748-1870 <585-748-1870>  *
>
> *     5115 South Hill Road ~ Canandaigua New York 14424*
>
> *www.solarandwindfx.com <http://www.solarandwindfx.com> ~ E-mail:
> chris at solarandwindfx.com <chris at solarandwindfx.com>*
>
>
>
>
>
>
>
>
>
>
>
>
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to
> exist
>                      when you take away from those who are willing to work
> and give to those who would not."
>
>
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
> *Sent:* Wednesday, April 23, 2014 11:36
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Stainless NEMA4x load center
>
>
>
> See my other response, but you should definitely consider SolaDeck in this
> case. You want SolaDeck Model 0786-41. Make sure you order the correct
> breakers, bus bars, and Neutral terminal block.
>
>
>
>
> http://www.rstcenterprises.com/soladeck/products/1741_combiner_enclosure.phtml
>
>
>
> ​The attached picture is the Soladeck on my 3-string ​Enphase system at
> home (note: neutral block was not on DIN rail yet). There are four neutrals
> on the bottom of the N block because I center-fed one inverter string, so I
> had four sets of Enphase cable coming into the box, which is admittedly a
> little tight. If you need to do this, I recommend transitioning to THWN in
> a separate combiner and just bringing in three strings through one or two
> conduits.
>
>
>
>
>
> ​[image: Inline image 1]​
>
>
>
> Jason Szumlanski
>
> ​Fafco Sola
> ​r​
>
>
>
> On Wed, Apr 23, 2014 at 11:17 AM, Kirpal Khalsa <solarworks at gmail.com>
> wrote:
>
> Drake.....we want it to mount flush to the slope of a sloped roof....The
> NEMA 3R are supposed to be mounted vertically....This is for a large
> residential Enphase system and we wanted to combine the circuits on the
> roof and bring one set of conductors down.....
>
> I did find one custom made by Eaton(Cutler Hammer), but....$952 my cost is
> too much..I have had them make me one out of fiberglass in the past but it
> is about 3 years into its roof mount life and showing signs of UV
> degradation...looking for other options....I think i will dig a little
> deeper at Midnite Solar.....They may have something....Theirs and Outback's
> PV combiners are rated to be mounted at a slope....i think it is down to 14
> degrees pitch (3/12)
>
> Thanks.
>
>
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified PV Installation Professional
> Renewable Energy Systems
> www.oregonsolarworks.com
>
> 541-218-0201 m
> 541-299-0402 o
>
>
>
> On Wed, Apr 23, 2014 at 8:11 AM, Drake <
> drake.chamberlin at redwoodalliance.org> wrote:
>
> That would be a nice piece of hardware. Is there any reason you can't use
> a NEMA 3R panel?  They are used on roofs quite a bit, and are readily
> available.  The Square D, 8 space, outdoor box should work in most rooftop
> environments for the purpose you describe.
>
>
> At 06:18 PM 4/21/2014, you wrote:
>
> Hello Friends!
> Anyone have a lead for* NEMA 4x* stainless load centers (electrical
> panel)? Â Looking for 4 circuit version rated at about 60-100A @ 240VAC.
>
>
> Would like to use it for rooftop combiner for 3 Enphase inverter output
> circuits.
> Thank you!!
>
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified PV Installation Professional
> Renewable Energy Systems
> www.oregonsolarworks.com
> 541-218-0201
>
> ______________
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140423/343d672f/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 527706 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140423/343d672f/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.jpg
Type: image/jpeg
Size: 2759 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140423/343d672f/attachment-0018.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 2593 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140423/343d672f/attachment-0019.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 130249 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140423/343d672f/attachment-0019.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.jpg
Type: image/jpeg
Size: 2415 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140423/343d672f/attachment-0020.jpg>