[RE-wrenches] Rapid shutdown for pole mounts

boB at midnitesolar.com boB at midnitesolar.com
Fri Apr 18 14:30:12 PDT 2014


Bill Brooks should probably respond to this also, but reading the NEC, 
it looks like if the wires
do not go inside the building to run more than 5 feet (as the crow 
flies), the the rapid disconnect
does not apply.    OR, less than 10 feet from the array IF the PV is 
mounted on that building.

boB



On 4/18/2014 1:34 PM, Aaron Mandelkorn wrote:
> The rapid shutdown language is so confusing. When looking at the rapid shutdown language, does PV systems "on" a building refer to only situations where the array is on a building; or does it include DC conductors as well. For example, if the DC conductors from a pole mounted array run up the side of a building before punching in to the inverter, does this require rapid shutdown?  Is this PV system considered "on" a building?
>
> Aaron
>
> Aaron Mandelkorn
> Owner/Solar Specialist
> Renewable Energy Outfitters
> 719-221-5249
> 970-596-3744
> www.reosolar.com
> reosolar at gmail.com
>
>