[RE-wrenches] Huge battery bank recommendation
Ray Walters
ray at solarray.com
Tue Mar 11 08:05:30 PDT 2014
Consider the HUP Solar One battery, the 125-33. It has 2490 AH at the
20 hr rate. The warranty is for 2100 cycles to 80% DOD. Also most of
the jumpers are included (bus bars within each 12 v group)
We've had nothing but happy customers since we started using the HUPs.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/11/2014 8:01 AM, penobscotsolar at midmaine.com wrote:
> Mac, for this type of large system we typically use Surrette/Rolls
> 2YS31.They are 2430 ah. When we get into battery banks this large we
> typically only run two cells deep (front to back) for ease of maintenance.
> I hope your customer has some free time on their hands for maintenance.
> Remember, Surrette deep cycle batteries demand a higher than most charge
> rate or you will find the life of the cell will be significantly shorter
> than with proper charging. I'm sure your local battery distributor or
> Jamie Surrette can send you the tech stuff on these batteries. Any way it
> goes, this is a very big battery bank. Good luck!
>
> Daryl DeJoy
> NABCEP Certified PV installer
> Penobscot Solar Design
>
>
>
>> Good point Jason. To clarify this is a 48V system.
>>
>> Thanks
>>
>>
>> On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski
>> <jason at fafcosolar.com>wrote:
>>
>>> Not that I have an answer for you, but I'm curious, too. You need to
>>> specify voltage to get a good answer.
>>>
>>> Jason Szumlanski
>>>
>>> Fafco Solar
>>>
>>>
>>>
>>>
>>>
>>> On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis <maclewis1 at gmail.com> wrote:
>>>
>>>> Hi wrenches,
>>>>
>>>> I am consulting on a job that requires an 8000 Ahr battery bank. This
>>>> is
>>>> quite a bit beyond my normal battery bank realm. What would you
>>>> recommend
>>>> for this?
>>>>
>>>> Thanks in advance
>>>>
>>>> --
>>>>
>>>>
>>>>
>>>> Mac Lewis
>>>>
>>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> *"Yo solo sé que no sé nada." -Sócrates*
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list