[RE-wrenches] Programmable Battery Charger
Jarmo.Venalainen at schneider-electric.com
Jarmo.Venalainen at schneider-electric.com
Tue Dec 16 12:35:10 PST 2014
Hi:
I'm enjoying learning many new ways of looking at things and of practical
solutions on this forum. In that spirit, the only thing I would add to
this discussion is that the power factor as seen by the AC source will be
very poor. In that regard, the larger the caps, the more stable the "DC"
voltage, but the poorer the PF.
This will show up as much lower charging efficiency due to the way in
which AC current is drawn by the bridge rectifier/capacitor circuit.
Here's an actual graph of how a bridge rectifier connected to a capacitor
draws AC current,
The graph is from my past life a couple of decades ago back when I was
studying. It's not a conventional phase-shift PF problem, but rather a
form factor PF problem. It shows the current drawn by a 13" PC monitor of
that era, before PF correction was mandated for all new products. In this
example the 'crest factor', (peak current as measured versus what it could
have been if the current was drawn throughout the AC pulses, was about
4x). Depending on the size of capacitor, it can be as high as 7x.
The practical effect on the wires and devices including the diodes and
charge controller, is that a lot of heat is generated in their power
components. The source of the energy for that heat is the AC source and
in cases where the AC source is a generator that translates to much higher
fuel consumption, (in some cases over 30% more).
Out of my tests back then, I also discovered one practical recommendation.
If you are using bridge rectifiers connected to capacitors, do not have
any length of wire and in particular no loop area in the wires between the
bridge rectifier and capacitors. Having wire/loop area introduces
inductance into the circuit which behaves somewhat like an ignition coil
due to the high speed reverse recovery period of the diodes; and this
happens four times every AC cycle. Given the right conditions the voltage
spikes caused by that inductance/ignition coil like effect will make short
work of the diodes and other components which are on the circuit.
The voltage spikes wont be a problem if the bridge rectifier is as close
as possible to the capacitors, but due to reverse recovery effect, you'll
still be stressing the parts and heating wires.
In my opinion, its ok to do this, but I wouldn't push power levels to
anywhere near the limits of components and devices.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Development Specialist - Senior
Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
"boB at midnitesolar.com" <boB at midnitesolar.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:
12/16/2014 11:16 AM
Subject:
Re: [RE-wrenches] Programmable Battery Charger
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
Larry, Pitfalls ?
The biggest pitfall I would say is if you have a VERY stiff grid.
If your Voc is say, 170V DC and the CC current limits it output at say,
169 V DC,
they you are going to need to add an input power resistor of a couple Ohms
to
help cushion the input to be more like a PV module. A lot of times, the
grid is
not nearly this bad, especially generators.
Also, If you are going to do this, I would NOT use Solar mode but instead
try
Hydro mode set to Manual MPP voltage. First start the MPPV at something
just
less than Voc or maybe, say, 160 VDC. Then, from main STATUS screen, you
can
adjust the input voltage up and down by pressing the Soft-Right or
Soft-Left
keys respectfully. (upper right and upper left keys). Then you can
manually get
a feel for what it should be set for.
The Classic 200 is the only CC of ours that I would use. The 250 would
work but the
200 is much more suited. I wish there were a real charger that one could
buy that was
isolated, and we have never really advocated MPPT charge controllers for
this but
in a pinch, they always seem to work find. Never did add a "DT" mode
(after Daryl
Thayer of course), but this hydro mode seems to work OK.
If you want to let it sweep but setting it to 3 minutes (or higher) that
will also work.
If you do that, set the minimum input voltage. Something like 140V or so
will keep
it from dropping the input voltage too low and either bogging down the
input source
and the rectifier bridge (especially generators)
You can also set the INPUT current limit in the LIMITS menu. This was for
hydro
in particular. Either limit can help reduce Isc or bogging down issues.
The other pitfall is that it is NOT galvanically isolated so you should be
very careful.
We use an X240 equivalent transformer to keep the batteries going in our
burn in
rack using 2 Classic 200s and it works great.
Also, use a nice and strong full bridge rectifier so that it applies 120
Hz instead of
60 Hz to the input. That is much easier on the input capacitors and
things and just
makes it work smoother. There are input capacitors (filtering) on most
charge controllers.
Again, in a pinch this seems to work but watch that input max power point
voltage to make
sure it is not too high compared to the Voc. If there isn't enough
voltage spacing between
the two (stiff AC source) then the control isn't going to be very smooth
and might risk
letting the smoke out.
What ever you do here, be very careful what you touch !
boB
On 12/16/2014 6:39 AM, Larry wrote:
I must have missed the prior discussion about using PV CC. The concept
sounds good but how many of you have done this and are there any pitfalls
to be aware of? If I use a 20 amp bridge I should be able to produce 80
amps @ 14.4V. For continuous operation, will I need a large heat sink on
it?
How does the unfiltered full wave peak voltage affect the CC over time?
Are they (specifically Midnite) really designed to handle input waveform
like this? I like this idea, especially if I can stack the controllers.
Thank you,
Larry
On 12/15/14 6:51 PM, jay peltz wrote:
Hi Kirk,
If you use a 200vdc midnight CC you'll have no issues.
When you rectify 120vac its up around 166vdc
( uses the peak vac which is around 170vac.)
For a 150vdc max controller ( midnite 150) or a 144vdc ( outback FM) then
a buck transformer or standard transformer is the trick to reduce the AC
and hence the DC for these lower voltage units.
jay
peltz power
On Dec 15, 2014, at 5:38 PM, Kirk Herander wrote:
This has been discussed on this list in years past. It is possible to use
an outback charge controller as a battery charger. You need to put the 120
AC into a bridge rectifier, then feed the 120 DC into the controller’s PV
input. So you’ll have an 80 amp battery charger.
Kirk Herander
VT Solar, LLC
Proven PV provider since 1991
www.vermontsolarnow.com
dba Vermont Solar Engineering
NABCEPTM Inaugural Certificant
VT RE Incentive Program Partner
802.863.1202
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Dan Tittmann
Sent: Monday, December 15, 2014 8:18 PM
To: info at windsine.org; RE-wrenches
Subject: Re: [RE-wrenches] Programmable Battery Charger
You can manually adjust Iotas with tweaking the potentiomiters while
monitoring it with a god volt meter. But no time adjustment.
Daniel
Daniel Tittmann
CTO
Greenwired
www.greenwired.com
daniel at greenwired.com
707-923-2001 (office)
707-206-5088 (Cell)
On Mon, Dec 15, 2014 at 4:21 PM, Windsine Inc. <windsine at gmail.com> wrote:
Check out Argus Technologies.
RoyR
On Dec 15, 2014 4:01 PM, "Larry" <larry at starlightsolar.com> wrote:
Wrenches,
Does anyone know of a 120/12 volt battery charger that can be programmed
for absorb and float voltage and time in absorb mode? I have been needing
this product for many years but I can only find it in inverters with built
in chargers from Magnum, Outback, and Xantrex.
--
Thank you,
Larry Crutcher
Starlight Solar Power Systems
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141216/59630162/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 43445 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141216/59630162/attachment-0004.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14092 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141216/59630162/attachment-0001.jpe>
More information about the RE-wrenches
mailing list