[RE-wrenches] Aux Output on Outback Devices
jay peltz
jay at asis.com
Fri Dec 5 16:25:20 PST 2014
Hi William
Supposed to be.
I've tried them with too large of a relay and wouldn't work ( the relay that is). Dead short would be the same.
But i did have a VFX 3648 many years ago that had 48v on the aux output. Stumped the hell out of outback. While talking to tech, they had me short the aux wires, and poof 1 dead inverter.
Jay
Peltz power
> On Dec 5, 2014, at 4:19 PM, "William Miller" <william at millersolar.com> wrote:
>
> Friends:
>
> I suspect my employees may have fried a VFX3648 recently by shorting the Aux output leads. Does anyone know if the FX inverter Aux output is supposed to be current limited?
>
> Thanks,
>
> William
>
>
> <image003.jpg>
> Lic 773985
> millersolar.com
> 805-438-5600
>
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray Walters
> Sent: Friday, December 05, 2014 3:08 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] common ground on fm80 aux output?
>
> I don't believe the aux is PWM. It should be a straight 12 v 200 mA output as I recall. Its just enough to run a battery fan, or a 12 v relay. You shouldn't need anything else. Being current limited, it doesn't even need a fuse.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141206/d565647e/attachment-0001.html>
More information about the RE-wrenches
mailing list