[RE-wrenches] High specific gravity
Mac Lewis
maclewis1 at gmail.com
Tue Aug 12 18:54:48 PDT 2014
Hello wrenches,
I just went on a service call for a new client. He had a bank of 4 year
old Interstate L16HCL batteries, 2 strings of 8, 48V system, 840Ahr. We
went through the batteries and got specific gravity on all of the cells
post-equalization. I was a bit surprised to see some very high numbers ie
over 1.32 for the specific gravities (higher than my refractometer goes).
The specific gravities were all over the place, but I haven't seen numbers
this high. I don't have a great explanation. He has a stacked 3648 VFX
Outback system, and the set-points were 58.8V Absorb for 2 hours, and 62V
Equalize for 2 hours. He has a decent amount of solar (about 3400W) and a
1000W wind generator.
Any ideas why the specific gravity is so high on some cells? Also, is
there anything wrong with having SG this high, post-equalization? For this
very standard battery, what settings do you go with (Bulk, Absorb, Float,
Eq, and times for Abs and Equalization).
Thanks in advance
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140812/d4c1ed1c/attachment-0001.html>
More information about the RE-wrenches
mailing list