Friends:
I am working on an off-grid system that includes a Sunny Island Mini-grid
and some Tristar 600 volt charge controllers. Everything is interconnected
in 8 by 8 gutters around three sides of an equipment room. Wiring
includes 48 volt DC, 120/208 VAC, 400 plus volt PV feeders and CAT 5. All
of this wiring can coexist as THWN and MTW rated at 600 Volts, except the
CAT5.
We created a partition system by running ½ EMT and NMLT inside the gutter
to carry the CAT5, and the system works by maintaining separation and
preserving the aesthetic of the equipment room. It is a bit of a pain in
the butt, however, to run the EMT/NMLT in the gutter.
I got to thinking there has to be a better way. I contacted PV Cables, Inc,
and they found a CAT5e that has a jacket rating of 600 VDC. This is the
answer to my dilemma on this and on some non-PV industrial jobs. The only
down side is the wire is available in 1000 foot rolls at about $800.00 per
roll. I also worry about if the wire will accept standard RJ45 connectors.
I have ordered a sample.
I thought you all should know about this, which is why I am writing. That,
and Id like to know if anyone wants to split the cost of a roll. I need
about 200 feet. Please contact me off-line.
William Miller
Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140508/55a68c62/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140508/55a68c62/attachment-0002.jpg>
More information about the RE-wrenches
mailing list