[RE-wrenches] FW: Unusual problem with SMA TL inverter on metal roof
Marco Mangelsdorf
marco at pvthawaii.com
Wed Mar 26 15:21:02 PDT 2014
With SMA's assistance, we're replacing the two 10 kW TLs with non-TL SB US
inverters.
marco
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[re-wrenches-bounces at lists.re-wrenches.org] on behalf of August Goers
[august at luminalt.com]
Sent: Tuesday, March 25, 2014 8:41 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof
Hi Marco,
Did you ever make any progress on this issue? We're having an interesting
issue with one of the new Sunny Tri-Power inverters (a 24 kW unit in this
case) where we get an error "residual current too high." We've only done a
little troubleshooting so far but I don't think we have a ground fault.
Best,
August
Luminalt
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Friday, March 14, 2014 9:56 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof
Probably not.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of RE Ellison
Sent: Friday, March 14, 2014 1:24 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
roof
Is the metal roof grounded? Just a fast thought.
bob
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Thursday, March 13, 2014 10:31 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof
Friends,
We have run across an odd technical problem at our commercial install at a
laundromat on our island. Attached is the description of the issue from
SMA. We don't know much except that we are switch out the TL inverters to
the old style US inverters because SMA has no fix for the phantom ground
tripping. The issue is beyond our feeble understanding.
Any observations to share?
Thanks,
marco
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4336 / Virus Database: 3722/7186 - Release Date: 03/12/14
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4336 / Virus Database: 3722/7186 - Release Date: 03/12/14
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140326/fc37988d/attachment-0002.html>
More information about the RE-wrenches
mailing list