Hi Wiliam,

The max voltage rating of the M250 is 48V.   When you ran the compatibility
checker, did you use 154mv/°C?  You can either input the mV/°C or the
%/°C.  You will need to be sure that you convert the 0.154 to 154mV.


On Mon, Sep 30, 2013 at 12:24 PM, William Miller <william at millersolar.com>wrote:

> Nick:****
>
> ** **
>
> What is the upper voltage limit for the M250?  What happens when that
> voltage is exceeded?****
>
> ** **
>
> I am trying to use Siemens SP75 modules (two in series) and Shell
> SQ-150-PC. Below are the specs.  Note that two SP75s in series, if you
> multiply the voltages by two, is identical to the SQ-150 except for the
> temperature compensation.  I am not sure what to do with the temperature
> compensation value if I put two SP175s insereis.  Do you know?****
>
> ** **
>
> ** **
>
> *Qty*
>
> *Watts*
>
> *Ext*
>
> *Watts*
>
> *Pmax*
>
> *Vpmax*
>
> *Ipmax*
>
> *Isc*
>
> *Voc*
>
> *Temp Coefficient of Voc*
>
> Siemens PC4JF (Same as the SP75?)****
>
> 12****
>
> 75****
>
> 900****
>
> 75****
>
> 75****
>
> 17****
>
> 4.4****
>
> 4.8****
>
> 21.7****
>
> -0.077****
>
> Shell SQ-150****
>
> 3****
>
> 150****
>
> 450****
>
> 150****
>
> 150****
>
> 34****
>
> 4.4****
>
> 4.8****
>
> 43.4****
>
> -0.161****
>
> ** **
>
> Our record low is -10 C and average high is 38C.****
>
> ** **
>
> If I enter the data for the Shell, the calculator shows they are
> compatible with the M250.  Entering the data for two SP75s using -0.077 for
> Temp Comp (SP75) the tool says not.  If I use double (-0.154), then the two
> SP75s are compatible.  What is your determination?****
>
> ** **
>
> Thanks,****
>
> ** **
>
> William****
>
> ** **
>
> ** **
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Nick Soleil
> *Sent:* Monday, September 30, 2013 9:56 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Using legacy modules on micro-inverters****
>
> ** **
>
> Hi wrenches,****
>
> The M250 is not limited to 60 cell modules only.  The M250 has an expanded
> voltage window which will allow for it to be paired with a wider range of
> modules.  Enphase has an online module compatibility calculator which can
> be used for checking a specific pairing in a specific location, at:
>
>  http://enphase.com/module-compatibility-calculator-m250-update/.  ****
>
> Keep in mind that many of the high efficiency, higher voltage, 72 cell
> modules will not be compatible.****
>
> ** **
>
> ** **
>
> On Sat, Sep 28, 2013 at 6:45 AM, Jay Peltz <jay at asis.com> wrote:****
>
> Hi Bill****
>
> ** **
>
> Is there a new M250?****
>
> Enphase shows the 250 at 48vdc max and states 60 cell only modules. ****
>
> ** **
>
> That would be nice if it did both****
>
> ** **
>
> Jay****
>
> ** **
>
> Peltz power. ****
>
> ** **
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

*
*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/>

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsoleil at enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130930/b236527f/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1981 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130930/b236527f/attachment-0004.jpg>


More information about the RE-wrenches mailing list