Eaton just announced some safety switches with shunt trip that may work
for you- Google: Eaton TD008003EN to get the datasheet.
TD008003EN
On 2013/9/24 11:12, Karl Jaeger wrote:
>
> Greetings Esteemed Wrenches,
>
> We are building a 35.75kW project with (6) Power One 6000's. The
> service is a 240 delta. The utility is requiring (late in the game)
> that if one leg of the service is lost, all inverters must shut down.
> Of course, we have two inverters that do not shut down in that
> circumstance because they are only tied into the other two phases. SMA
> has a good (cheap) option to deal with this, SMA Power Balancers. With
> other inverters this can be accomplished by installing an ATS with an
> integrated controller by programming in the unacceptable phase
> imbalance (expensive). Does anyone have experience with this
> requirement and/or have a good (cheaper) solution?
>
> Thank you in advance!
>
> Karl Jaeger
>
> LightWave Solar
>
> Nashville, TN
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130924/d96219fd/attachment-0004.html>
More information about the RE-wrenches
mailing list