[RE-wrenches] Charging voltages
Jesse Dahl
dahlsolar at gmail.com
Mon May 13 22:03:29 PDT 2013
I notice when reading the flexmax 80 manual on-line that they recommend the array V be 12v to 24v higher then nominal battery V. The system in question is only 7v above nominal.
So what problems am I going to hear about the next time this dude calls me?
This system is GDI with battery backup in an area with one or two day long outages per year.
Jesse
Sent from my iPhone
On May 13, 2013, at 9:51 PM, Kirpal Khalsa <solarworks at gmail.com> wrote:
> Jesse.....why wouldn't you wire at least 2 modules in series....this way you have less breakers to deal with, less cord grips if paralleling in a combiner box, less homerun cables to the combiner and you will also benefit from greater energy harvest in your MPPT conversion particularly during cold weather....
> If you go with 1 module strings and have hot weather your voltage sag in the summer you will be on the low edge of voltage window to properly charge a 24V battery bank.....
> i would check the charge voltage recommendations from the battery manufacturer for proper charging parameters....usually the voltage recommendations call for lower voltages than FLA batteries...may be helpful for being able to charge your sealed batteries from a single module. It is still borderline...
> I have always believed that the 60 cell modules were a bit on the low side for 24V battery charging. In the past that is what the 72 cell modules were for....but those are fewer and farther between these days, except int he larger 300+ watt modules....
> If you had 9 modules i would even go with strings of 3....or if you want to get really efficient you could wire in strings of 4 with the Midnite Solar Classic 200 charge controller.....you would definitely be bumping into amperage limits.....but that is ok...
> good luck...
>
>
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified PV Installation Professional
> Renewable Energy Systems
> www.oregonsolarworks.com
> 541-218-0201 m
> 541-592-3958 o
>
>
> On Mon, May 13, 2013 at 7:34 PM, Jesse Dahl <dahlsolar at gmail.com> wrote:
>> Hello,
>>
>> I'm interested in charging voltages for AGM batteries. After my visit to the site mentioned in the battery box thread, I was thinking about the system.
>>
>> New install, 8 solarworld 255s charging a 24V battery bank through a outback FM80 (MPPT) All 8 modules in parallel.
>> VOC - 37.8
>> VMP - 31.4
>> ISC - 8.66
>> IMP - 8.15
>>
>> I'm interested in the setpoints people use for AGMs because it seems like this might be cutting it close to the setpoints based on the array voltage. Since the system is using a MPPT controller would it be better to increase the array voltage?
>>
>> Battery bank is 6 12V 245ah east penn bats wired 3 strings of 2.
>>
>> I haven't used sealed batteries outside my fish house and boat so I'm looking for some detailed info if I can get it.
>>
>> Thanks a lot!
>>
>> Jesse
>>
>>
>> Sent from my iPhone
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130514/ac9bb0b3/attachment-0004.html>
More information about the RE-wrenches
mailing list