[RE-wrenches] Fuse sizing in battery circuits

Ray Walters ray at solarray.com
Sat Apr 6 10:13:34 PDT 2013


Hi Phil;

I'm not sure what 690.71 adds over the long standing requirements of 
110.9 and 240.86.  We've always complied with the interrupt rating 
requirements.  Old Ananda power centers had QOU breakers that only had 
an interrupt rating of (I believe) 5000 amps DC, so a class T fuse was 
added to the circuit as well.  The power center is always installed 
'adjacent to the batteries', so we've always met that requirement as well.
Nothing in the NEC specifies an actual distance to the batteries the 
OCPD needs to be, and it doesn't specify that each series string have 
separate OCPDs.
I'm glad to hear that Outback has a solution; Midnite has also had that 
type of protection available in their battery enclosures for some time 
as well.  None of this deals with the truly high fault currents 
available from industrial fork lift batteries though. When using AGMs, 
you can just put a class T fuse on the battery terminal.
The only battery I've ever seen that actually protected against a short 
circuit across its own terminals was in my kid's Barbie Jeep.  It had a 
fuse integrated right into the top of the sealed battery.  Maybe as the 
industry progresses towards other battery chemistries, we will see more 
integrated OCPDs that are only found on kid's toys today.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/6/2013 8:29 AM, Phil Undercuffler wrote:
> Ray,
>
> 690 does offer the protection, it's just that most maufacturers 
> haven't made it easy.
>
> 690.71 Installation
>
> (C) Current Limiting. A listed, current-limiting, overcurrent device 
> shall be installed in each circuit adjacent to the batteries where the 
> available short-circuit current from a battery or battery bank exceeds 
> the interrupting or withstand ratings of other equipment in that 
> circuit. The installation of current-limiting fuses shall comply with 
> 690.16.
>
>
> The telcom industry has been doing this for years.  Their norm is to 
> have each string of batteries on a shelf, and terminate at a breaker. 
>  Each string then is combined at a bus bar or plate, to help ensure 
> equal current on each string.  The loads and charging sources all come 
> to that same bus bar.  It has some advantages, as individual strings 
> can be monitored and serviced without taking the entire system down.
>
> FWIW, OutBack makes a battery rack for AGM batteries with series 
> string overcurrent and disconnects on every string.  It's also to my 
> knowledge the first UL1741 Listed device available -- the other stuff 
> I've seen is either not listed, or is trading on old 508a standards. 
>  AGMs might not be for every installation, but for jobs where they are 
> appropriate this could be a good, code-compliant solution.
>
>
> Phil Undercuffler
> OutBack Power
>
>
>
>
> On Friday, April 5, 2013, Ray Walters wrote:
>
>     I just finished a rewire and we kept the Ananda power center,
>     Allan :-)
>     Back when we used class T fuses more they were always over sized
>     relative to Heinemann breakers.
>     400 amp class T fuse = 250 amp breaker= 4/0 cable
>     200 amp class T fuse = 175 amp breaker= 2/0 cable
>
>     I still think class T fuses are superior in some ways to breakers:
>     they have better interrupt capacity and trip faster in a short
>     circuit condition.
>
>     However, If you spend too much time thinking about and looking at
>     the trip curves, you'll break your brain and special order some
>     weird fuses and breakers.  (anybody need a 350 amp class T fuse?)
>      Just follow the inverter manufacturer's recommendations and all
>     will be well.
>     On the other hand, William has brought up a topic I have harped on
>     for years:  Having the OCPD in the cabinet doesn't protect the
>     majority of the circuit.  Class T fuses at the battery terminals
>     do, but they're not rated for the corrosive environment.  I have
>     thrown a few class T fuses away that had acid eating away at the ends.
>     I don't have the solution, but I will continue to point out that
>     this is a real problem. Dropping a wrench across the battery
>     terminals can lead to a spectacular failure that not only can
>     cause a fire, but might even cause a battery explosion, yet NEC
>     offers no protection.
>     We use insulated wrenches from experience, and hope for the best.
>
>     R.Ray Walters
>     CTO, Solarray, Inc
>     Nabcep Certified PV Installer,
>     Licensed Master Electrician
>     Solar Design Engineer
>     303 505-8760
>
>     On 4/5/2013 8:29 PM, William Miller wrote:
>>     Friends:
>>
>>     Good topic.  Some questions:
>>
>>     1. Most manufacturer's present an installation guide that shows
>>     one OCPD in the battery circuit and that is in the BOS cabinet. 
>>     This means the battery leads are unprotected.  Do we need an OPCD
>>     at the battery terminals?
>>
>>     2. Class T fuses are generally recommended for this application. 
>>     The data shows them as "fast acting."  Is this a problem?  Will
>>     they act too fast and open during normal surge loads?
>>
>>     Thanks in advance!
>>
>>     William Miller
>>
>>
>>
>>
>>
>>>     Troy,
>>>
>>>     Overcurrent device size is matched to the conductor size. The
>>>     inverse time constant nature of an overcurrent device can
>>>     typically handle the surge currents as long as conductor sizing
>>>     has truly been done correctly for the conductor. Circuit
>>>     breakers are preferred to fuses because they can be reset.
>>>
>>>     There has been volumes written on this issue. The constant
>>>     current at lowest battery voltage should be used, plus the ac
>>>     ripple content on the battery circuit. This is usually a much
>>>     larger conductor than your average designer will plan for. The
>>>     best thing is to look at Midnight, Outback, and Schneider and
>>>     see what size overcurrent devices they require for their
>>>     products. That will give you a good clue as to how to size the
>>>     conductor and overcurrent device.
>>>
>>>     Bill.
>>>
>>>     *From:* re-wrenches-bounces at lists.re-wrenches.org
>>>     <javascript:_e({}, 'cvml',
>>>     're-wrenches-bounces at lists.re-wrenches.org');>
>>>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>>     <javascript:_e({}, 'cvml',
>>>     're-wrenches-bounces at lists.re-wrenches.org');>] *On Behalf Of
>>>     *Troy Harvey
>>>     *Sent:* Friday, April 05, 2013 3:38 PM
>>>     *To:* RE-wrenches
>>>     *Subject:* [RE-wrenches] Fuse sizing in battery circuits
>>>
>>>     I've got a question about battery string fusing. Typically we
>>>     size the wire from the batteries to the inverter based on
>>>     continuous rating procedures (max power/efficiency)*125%.
>>>
>>>     However a 6kW inverter, can peak at 12kW for 5-10 seconds,
>>>     doubling the source current. That is no big deal for the wire,
>>>     because it is a short time frame... little heat will be
>>>     generated. However, in fusing the sub-strings, you need to
>>>     account for that peak surge current so you don't blow fuses all
>>>     the time. But if you put a 500-1000 amp fuse on a 4/0 wire,
>>>     above the max surge draw of the inverter, the wire will be
>>>     under-protected for its ampacity rating. Any thoughts on the
>>>     catch-22?
>>
>>
>>     _______________________________________________
>>     List sponsored by Home Power magazine
>>
>>     List Address:RE-wrenches at lists.re-wrenches.org  <javascript:_e({}, 'cvml', 'RE-wrenches at lists.re-wrenches.org');>
>>
>>     Change email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out participant bios:
>>     www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130406/e61e0a75/attachment-0004.html>


More information about the RE-wrenches mailing list