Thanks for the succinct explanation Nick. I look forward to the fix. Like
you, I believe this is happening with other inverters, but lacking the
level of monitoring available with Enphase, people just aren't aware it is
happening.

Daryl



> Hi wrenches,
>
> The frequency out of range issue is being caused by some utility meter's
> communication "ping".  This ping is actually affecting the utility voltage
> and frequency, and can be viewed with a power quality analyzer.  It is
> highly likely that this is affecting a wide variety of utility-interactive
> inverters, but is only noticeable with the Enphase systems; due to the
> high
> level of visibility that our Enlighten monitoring and reporting provides.
>
> These changes required that the software undergo a new certification
> process. We have completed our CSA certification of the new software, and
> are validating it's functionality before pushing out the solution to our
> entire population of microinverters.  We are in the process of beta
> testing
> the software fix, and are hoping to have this resolved in February.
>
> Thank you for your patience as we work to resolve this issue.
>
>
> On Tue, Feb 5, 2013 at 9:24 AM, <penobscotsolar at midmaine.com> wrote:
>
>> Dave,
>>    It doesn't happen often, and the longest I've seen him stay "down" is
>> about a half hour, but it seems to get progressively worse as time goes
>> on for some reason (initially only the five minutes, but longer down
>> times lately). This particular customer is difficult and picky, to
>> boot. I hope yours is a bit kinder. Mine seems to think we did him an
>> injustice of monumental proportions.
>>    We have had the utility out there logging events, meetings with the
>> utility and another solar company in Maine to discuss all this, and
>> have kept Enphase in the loop throughout. Enphase has responded in a
>> responsible and reasonable manner throughout.
>>    If you want to discuss this with Enphase, call and ask for Bret. He's
>> the engineer I previously dealt with, although he is second tier, he is
>> accessible.
>>
>>
>>
>>
>> > Thanks Daryl. Does your system also sometimes stay off for longer
>> periods
>> > sometimes? My clients system can stay off for up to 64 minutes.
>> >
>> > Dave
>> >
>> > -----Original Message-----
>> > From: re-wrenches-bounces at lists.re-wrenches.org
>> > [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
>> > penobscotsolar at midmaine.com
>> > Sent: Tuesday, February 05, 2013 12:01 PM
>> > To: RE-wrenches
>> > Subject: Re: [RE-wrenches] Enphase "AC Frequency out of Range"
>> >
>> > Dave,
>> >   We have been having the same problem with an Enphase system in
>> Maine. I
>> > have been dealing directly with the third tier engineers at Enphase
>> and
>> > they
>> > are working on a software fix for this. The"event" itself is only a
>> > fraction
>> > of a second but IEEE requirements are that the inverter shut down for
>> five
>> > minutes. I only found out about this problem when it started for this
>> > customer. It sems that Enphase has already addressed the problem with
>> a
>> > software fix for the M-190's. The M-215 fix should come, according to
>> > Enphase, by the end of March. It will be automatically downloaded
>> through
>> > the Enlighten router.
>> >    It's a known issue with Smart Meters with Enphase, but should be
>> > reconciled soon.
>> >
>> > Daryl DeJoy
>> > NABCEP Certified PV installer
>> > Penobscot Solar Design
>> > www.penobscotsolar.com
>> >
>> >
>> >
>> >> Wrenchsters,
>> >>
>> >>
>> >>
>> >> I have an Enphase 7.5kW system on a residence with utility Smart
>> >> Metering, both the PV Production Meter as well as the utility billing
>> >> meter being "read" every hour. This system has experienced many "AC
>> >> Frequency Out Of Range" events since the system was installed. Below
>> >> is copied the Enphase Event message. This particular event was for 5
>> >> minutes. Most of the events (all events are AC Frequency Out Of
>> Range)
>> >> last 5 to 10 minutes but occasionally they have lasted from 45
>> minutes
>> >> to
>> > 64 minutes.
>> >>
>> >>
>> >>
>> >> My question is: Could the use of the smart metering increase the
>> >> likely hood that AC Frequency events happen? Or is this just a
>> >> coincidence and that we are dealing with fluctuating utility power AC
>> >> Frequency issues?
>> >>
>> >>
>> >>
>> >> <<
>> >>
>> >>
>> >>
>> >> Started on: Mon February 04, 2013 12:49 PM EST
>> >>
>> >> Cleared on: Mon February 04, 2013 12:54 PM EST
>> >>
>> >>
>> >>
>> >> Recommended action
>> >>
>> >>
>> >>
>> >> This condition should correct itself. No action is required.
>> >>
>> >> Details
>> >>
>> >>
>> >>
>> >> The microinverter reports that the frequency coming from the utility
>> >> is either too low or too high as specified by applicable regional
>> > standards.
>> >>
>> >>
>> >>
>> >> AC frequency is the frequency at which voltage varies on the utility
>> >> grid.
>> >> Frequency Out of Range events are usually transient and
>> >> self-correcting by the utility.
>> >>
>> >>
>> >>
>> >> When the microinverter detects an out of frequency condition, it must
>> >> remain offline until the utility has been within acceptable limits
>> >> continuously for a short period of time (seconds to minutes, varies
>> by
>> >> region). If during that time the utility again exceeds or falls short
>> >> of acceptable limits, the five-minute timer must restart and the
>> >> microinverter may not begin producing power for an additional short
>> >> period following the last out-of-bounds condition.  >>
>> >>
>> >>
>> >>
>> >> Best,
>> >>
>> >> Dave
>> >>
>> >>
>> >>
>> >>
>> >>
>> >> David Palumbo
>> >>
>> >> Independent Power LLC
>> >>
>> >> 462 Solar Way Drive
>> >>
>> >> Hyde Park, VT 05655
>> >>
>> >> www.independentpowerllc.com
>> >>
>> >> Vermont Solar Partner
>> >>
>> >> 25 Years Experience, (802) 888-7194
>> >>
>> >>
>> >>
>> >> _______________________________________________
>> >> List sponsored by Home Power magazine
>> >>
>> >> List Address: RE-wrenches at lists.re-wrenches.org
>> >>
>> >> Options & settings:
>> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>
>> >> List-Archive:
>> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >>
>> >> List rules & etiquette:
>> >> www.re-wrenches.org/etiquette.htm
>> >>
>> >> Check out participant bios:
>> >> www.members.re-wrenches.org
>> >>
>> >>
>> >
>> >
>> > _______________________________________________
>> > List sponsored by Home Power magazine
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> > Options & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out participant bios:
>> > www.members.re-wrenches.org
>> >
>> >
>> > _______________________________________________
>> > List sponsored by Home Power magazine
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> > Options & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out participant bios:
>> > www.members.re-wrenches.org
>> >
>> >
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
>
> Cordially,
>
> *Nick Soleil*
>
> *Field Applications Engineer
> *
>
> *Enphase Energy*
>
> Mobile: (707) 321-2937
>
>
> **
>
> *Enphase Commercial Solar.*
> *Limitless.*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
>
> *
> *<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
>
> 1420 North McDowell
>
> Petaluma, CA 94954
>
> www.enphase.com <http://www.enphaseenergy.com/>
>
> P: (707) 763-4784 x7267
>
> F: (707) 763-0784
>
> E: nsoleil at enphaseenergy.com
>
> [image: nabcep logo] Certified Solar PV Installer #03262011-300
>
> “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
> to fission. And it just so happens that there’s an enormous fusion reactor
> safely banked a few million miles from us. It delivers more than we could
> ever use in just about 8 minutes. And it’s wireless! .”
>
> - William McDonough
>
>
>
> This email message is for the sole use of the intended recipient(s) and
> may contain confidential and/or privileged information. If you are not an
> intended recipient, you may not review, use, copy, disclose or distribute
> this message. If you received this message in error, please contact the
> sender by reply email and destroy all copies of the original message.
>
_______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>





More information about the RE-wrenches mailing list