[RE-wrenches] Wire sizing calculator online
Ray Walters
ray at solarray.com
Mon Feb 4 09:09:13 PST 2013
Hey Carl;
That's my spread sheet! Glad it was useful on the other side of the
world. William and I have discussed the development of these wire
sizing spread sheets for years, including adding temp compensation. I
recently did a full blown upgrade with current calculations that
corresponded to NEC 2011, alas that computer was taken, before I ever
backed it up. Maybe I should take another stab at it. I'll incorporate
your metric info too. I guess this is what they call "open source"
development.
Ray Walters
Solarray, Inc. (now in Denver)
On 2/3/2013 9:48 PM, Carl Emerson wrote:
>
> Hi William,
>
> I am unsure what others refer to, I have used the attached spreadsheet
> in the past, I think it originates from New Mexico. I have added a
> reference to cross sectional area.
>
> On the issue if resistance, I wonder how much cable is pure copper
> these days, we see a lot of cheap cable out of Asia that very likely
> has additives. I am guessing that one might need to go back to the
> supplier to be sure of resistance if that were possible.
>
> You will see in the spreadsheet reference to NEC 2005, chapter 9,
> table 8 -- this is very comprehensive and includes resistance -- among
> other places, it can be found nicely laid out here...
>
> http://www.buildmyowncabin.com/nec/nec2005_chap9_table8.html
>
> This is good for DC only I believe.
>
> I could ask contacts I have in Germany what they use, I would guess
> they have it tied down to the last ohm...
>
> Hope this helps
>
> Regards
> Carl Emerson
>
> Carl:
>
> You are very welcome.
>
> I'd be willing to provide a metric chart. I need some information to
> get started. In the US, practices are dictated by our NEC which
> provides the resistance values for standard wire gauges. By putting
> the values in the Code, it gives all parties a reference and
> (hopefully) avoids arguments about conflicting data.
>
> I downloaded the New Zealand Electrical Code of Practice (NZECP
> 51:2004) and did not find in it any resistance values. Is this the
> correct document to look in? Are resistance values in there and I am
> just not finding them? If the values are not in the NZECP, where do
> professionals in New Zealand look for the resistance values?
>
> There is a slight difference in resistance (impedance) between AC and
> DC circuits as listed in the NEC. I used the higher values to allow
> conformity in all cases. Let me know if there is a different
> consideration for AC versus DC in New Zealand.
>
> Do you know what other Metric based nations use for determining wire
> resistance values?
>
> Thanks in advance.
>
> William Miller
>
>
> At 04:32 PM 2/3/2013, Carl Emerson wrote:
>
> Hi William,
>
> Just a comment on the spreadsheet.
>
> You have made provision for Centigrade, being friendly to those
> outside USA.
>
> It would be nice to have reference to wire cross sectional area in mm²
> as AWG is foreign to lots of folks from outside the US who reference
> your site.
>
> I must say that your making information freely available over the
> years has assisted many.
>
> Regards
> Carl Emerson
>
> fcb06a.jpg
> 022 630 9689
> carl at solarking.net.nz <mailto:carl at solarking.net.nz>
> solarking.net.nz
> PO Box 305-130,
> Triton Plaza,
> Auckland 0757
>
> ------------------------------------------------------------------------
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
> *William Miller
> *Sent:* 4 February 2013 12:06 p.m.
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Wire sizing calculator online
>
> Todd:
>
> Thanks for the plug. The copy you have is outdated. Here is where
> you will find the new and improved version:
> http://millersolar.com/MillerSolar/Resources/_Resources.html
>
> What we created in the Miller Solar wire sizing spreadsheet is an
> opportunity to compare the voltage drop for all common wire sizes in
> one view so you can evaluate the tradeoffs for various scenarios.
>
> Questions or comments are appreciated.
>
> William Miller
>
>
>
> At 09:54 PM 2/1/2013, toddcory at finestplanet.com wrote:
>
>
> thank you... this is useful. do you have william millers calculator
> too? its attached in case you dont.
>
>
>
> todd
>
>
>
>
>
>
>
>
>
> On Friday, February 1, 2013 5:23pm, "Solarguy" <ntrei at 1scom.net> said:
>
> I stumbled onto this wire sizing calculator that gives NEC qualified
> data.
> Wikipedia had a link to it.
> http://www.cablesizer.com/
> Jim Duncan
> North Texas Renewable Energy Inc
> www.ntrei.com <http://www.ntrei.com/>
> NABCEP PV 031310-57
> TECL-27398
> ntrei at 1scom.net <mailto:ntrei at 1scom.net>
> 817.917.0527
> NABCEP Logo
>
>
>
> Sent from Finest Planet WebMail.
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com <http://www.avg.com/>
> Version: 8.5.455 / Virus Database: 271.1.1/5567 - Release Date:
> 01/29/13 19:34:00
>
> Miller Solar
> Voice :805-438-5600
> email: william at millersolar.com
> http://millersolar.com <http://millersolar.com/>
> License No. C-10-773985
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com <http://www.avg.com/>
> Version: 8.5.455 / Virus Database: 271.1.1/5579 - Release Date:
> 02/03/13 17:56:00
>
> Miller Solar
> Voice :805-438-5600
> email: william at millersolar.com
> http://millersolar.com
> <http://millersolar.com/>License No. C-10-773985
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130204/9befdfce/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 6354 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130204/9befdfce/attachment-0004.jpe>
More information about the RE-wrenches
mailing list