Dave Click daveclick at fsec.ucf.edu
Tue Nov 19 10:22:05 PST 2013


** *300.3(B) Conductors of the Same Circuit.* All conductors of the same 
circuit and, where used, the grounded conductor and all equipment 
grounding conductors and bonding conductors shall be contained within 
the same raceway, auxiliary gutter, cable tray, cablebus assembly, 
trench, cable, or cord, unless otherwise permitted in accordance with 
300.3(B)(1) through (B)(4) [which don't help here]. National Electrical 
Code 2008 Edition


On 2013/11/19, 12:38, August Goers wrote:
>
> Hi All --
>
> On a related note, I've become good friends with some of the 
> inspectors in San Francisco and they called me yesterday with a 
> question. Is it okay to run _individual_ DC conductors through EMT for 
> wire management purposes? We have always run paired positive and 
> negative conductors in conduit so the question had never occurred to 
> me. Obviously, you have to bond both ends of the conduit if it is over 
> 250 v. I know that AC would have induction issues with running 
> individual conductors but I'm not sure with DC.
>
> Thanks,
>
> August
>
> August Goers
>
> Principal
>
> Luminalt Energy Corporation
>
> o: 415.641.4000
>
> m: 415.559.1525
>
> www.luminalt.com <http://www.luminalt.com>
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org> 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of 
> *William Miller
> *Sent:* Monday, November 18, 2013 11:33 PM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] PV Wiring methods
>
> Bill:
>
> There is no need to stuff MC4 cables into standard conduit.  You can 
> either slot the pipe using our easy method or install bulkhead type 
> connectors.  The connectors are readily available.  I get them from PV 
> Cables in Northern California..
>
> Wire routing problems and some solutions can be found on our web-site:
>
> http://millersolar.com/MillerSolar/practices/PV_wiring/_PV_Wiring2.html
>
> Since the industry won't provide wire management solutions, we are 
> making our own.  Questions:  Just write or call.
>
> William Miller
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org> 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *frenergy
> *Sent:* Thursday, November 14, 2013 7:46 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] PV Wiring methods
>
> William, Bill....from another Bill,
>
>         Two things:  For the rest of us (maybe it's just me?!) that's 
> still trying to figure out how (or why) to stuff a MC4 connector into 
> conduit and my hesitation in using SS wire ties for fear of the sharp 
> edges cutting or chaffing into cables, I'm open for advice. Any wire I 
> use on the roof is rated for that type of service and I have some 
> off-grid systems that have been in the sun for some 25 years where the 
> wire still looks nearly new even when flexing it to look for 
> checking/cracks.  It seems the wire/insulation can take it, thus it 
> seems like the key to "wire management is to keep the wire from moving 
> and off the roof, secured to the racking, thus not compromising the 
> insulation.
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131119/01b74de5/attachment-0003.html>


More information about the RE-wrenches mailing list