[RE-wrenches] Enphase commercial
Holt Kelly
Holtek at sbcglobal.net
Thu Oct 3 12:53:35 PDT 2013
Be sure to read Enphase's tech sheet on center tap of branch circuits.
Holt E. Kelly
Holtek Fireplace & Solar Products
500 Jewell Dr.
Waco, TX 76712
<http://www.holteksolar.com/> www.holteksolar.com
254-751-9111
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nathan
Stumpff
Sent: Thursday, October 03, 2013 2:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase commercial
Hi Eric,
It is 25 inverters on a 20A circuit, but only on 208 three phase. Each micro
connects to the cable in an alternating way (L1/L2, then L2/L3, then L3/L1,
etc.) so with 25 micros there are either 8 or 9 micros on each combination.
9 x 1.0 A x 1.732 (square root of 3) x 1.25 = 19.48 A = 20 A breaker
Cheers,
-Nathan
--
Nathan J. Stumpff
NABCEP Certified PV Installation Professional #091209-175
NABCEP Certified Solar Heating Installer #032412-14
Project Manager | Arctic Sun, LLC
nathan at arcticsun-llc.com <mailto:nathan at arcticsun-llc.com> | (907)
457-1297
www.reina-llc.com <http://www.reina-llc.com/> | www.arcticsun-llc.com
<http://www.arcticsun-llc.com/>
<http://www.facebook.com/ArcticSunLLC>
From: re-wrenches-bounces at lists.re-wrenches.org
<mailto:re-wrenches-bounces at lists.re-wrenches.org>
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of SunHarvest
Sent: Thursday, October 03, 2013 10:52 AM
To: RE-wrenches
Subject: [RE-wrenches] Enphase commercial
Hey Wrenches & Nick Soleil (with whom I worked at APS for a time I
believe...),
I'm not familiar with Enphase commercial applications and am currently
working through a commercial design. Enphase, on their M215 datasheets claim
up to 25 micros per branch, at 1.0A each, with each branch terminating at a
20A breaker. By my calculations, 25 micros at 1.0A each (25A*1.25=31.25A)
need to terminate at a 40A breaker. Anyone know what I'm missing or know how
the 20A breaker design gets past the AHJ?
Eric Stikes
SunHarvest
(530) 798-3738
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131003/2ec55c4a/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 2272 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20131003/2ec55c4a/attachment-0006.png>
More information about the RE-wrenches
mailing list