[RE-wrenches] Generator automatic disconnect
Ray Walters
ray at solarray.com
Mon Sep 30 16:38:28 PDT 2013
3rd option would be to have a separate charger (IOTA) that just runs
from the generator. No pass through loads to the generator.
4th option would be to use a larger Kohler for backup. My experience is
that even if they don't think they'll need it, they eventually will
actually use it. Large off grid systems tend to creep ever larger.
I'd look at all the scenarios with pricing, and pros and cons. You'll
see what makes sense.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 9/30/2013 5:14 PM, William Miller wrote:
> Larry:
>
> Maybe a better approach might be to use an inverter with "Gen-support."
> That is unless a system already exists that does not have this feature.
>
> Plan B: use the gen start signal to disable one or more of the larger
> loads.
>
> I know this is not what you asked for, just trying inject some different
> ideas.
>
> William
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry
> Crutcher, Starlight Solar Power Systems
> Sent: Monday, September 30, 2013 1:02 PM
> To: RE-wrenches
> Subject: [RE-wrenches] Generator automatic disconnect
>
> Wrenches,
>
> I want to use the Ecogen 6kW generator on a large off grid system. The
> location has very few overcast or rainy days and the generator will rarely
> be needed. My concerns is nuisance tripping the generator output breakers if
> the household load exceeds 6kW. The power system control has a feature for
> reducing the AC current used to charge the batteries but does not have a
> feature for disconnecting the AC input based on input load.
>
> Does anyone have a solution for monitoring AC load from the generator and
> disconnect it if overloaded? It must automatically reconnect after a short
> timeout.
>
> Thank you,
> Larry Crutcher
> _____________
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list