[RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service
Brian Mehalic
brian at solarenergy.org
Mon Jun 17 11:05:09 PDT 2013
True, as mentioned 160 is not a standard size, but you also cannot use a smaller size for a load side connection, unless you can use/find equipment rated for continuous duty...then you'd only need a 125A OCPD.
Typos courtesy of my iPhone.
On Jun 17, 2013, at 1:33 PM, Pekka Laine <pekka at photonsolarpower.com> wrote:
> Dear Fellow Wrenches,
>
> We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A. We are landing those into a dedicated load center with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would need a 160A breaker. This also equals to the maximum we can backfeed into a 800A/800A Main Service on the load side according to the "120%" rule.
>
> The problem now is that we cannot locate any kind of 160A breaker or even a 160A fuse for a AC disconnect.
>
> Has anybody ever done this without doing a "line-side tap?" It is hard to believe that there wouldn't be an existing solution to landing maximum PV into a 800A service. Are we missing something?
>
> Any good ideas or comments would be appreciated.
>
> Sincerely,
>
> Pekka Laine
>
> President
> Photon Solar Power Inc.
> www.PhotonSolarPower.com
> Cell. 760-556-8170
> Toll Free 888-SUN-ACDC
> CA Lic. #933648
> NABCEP Certified PV Installer # 032611-174
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list