Jeremy,
Good point. Even under the 2008 NEC 690.64(B)(2) you can install up to a 40
Amp breaker on the load side as long as it is on the opposite side of the
input feed per 690.64(B)(7). Garrison, do you need a 60 A breaker?
I haven't used this product myself, but if the continuous output power is
indeed 4500 W then you'd be fine with a 25 or 30 A breaker.
Best,
August
*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *All Solar, Inc.
*Sent:* Wednesday, February 27, 2013 1:50 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection
There is an exception in NEC2011 regarding the point of connection. This
may not apply, but you could avoid the supply side. 4500W / 240V = 18.75 x
1.25 = 23.4A, well under the 120% rule. reference 705.12(D)(2)
Jeremy
All Solar
CO,USA
----- Original Message -----
*From:* Garrison Riegel <garrison at solarserviceinc.com>
*To:* 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
*Sent:* Wednesday, February 27, 2013 2:15 PM
*Subject:* [RE-wrenches] Conductor Sizing for Supply Side Connection
Wrenches,
On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A
service, and I’d very much appreciate some advice if y’all are willing.
Since the inverter output OCPD is required to be 60A we are looking at a
supply side connection, and I have two questions:
1. Before the point of interconnection the inverter output circuit
will first pass through the XW Power Distribution Panel and inverter
bypass, which is essentially a 60A breaker. The service disconnect for the
supply side connection will also be fused at 60A. Does the 120% rule apply
to the conductor between these two OCPDs? Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this
AHJ is on the 2008 NEC]
2. Can anyone recommend a reliable insulation piercing tap
connector? Or would you recommend something else entirely for a
residential supply side connection?
Thanks in advance,
Garrison
847-677-0950
Solar Service Inc.
------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130227/ff44f620/attachment-0003.html>
More information about the RE-wrenches
mailing list