[RE-wrenches] DC circuit breakers in parallel
bob ellison
reellison at gmail.com
Wed Feb 27 13:23:59 PST 2013
Makes me wonder how many dual breakers I have taken the handle tie off and
used as singles in the past. It has been several, and none with no internal
connections that I could find or notice, with the exception of longer rivets
holding them together.
Granted it has been a while since I have done that.
Later,
Bob Ellison
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John Berdner
Sent: Wednesday, February 27, 2013 2:06 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC circuit breakers in parallel
Larry:
The Code requires parallel breakers to be designed for this application
(internally ganged).
Just using a handle tie does not allow you to use the poles in parallel.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new
address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ryan
Sent: Wednesday, February 27, 2013 8:45 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] DC circuit breakers in parallel
Larry
Our 100 amp din rail is essentially 2 breakers in parallel. So in theory the
2 60 amp breakers "Could" work but. My concern would be that they may not be
tripped at the same time where they are not internally ganged. I can't say
"Go Ahead" but.
Ryan
--
Ryan Stankevitz
Technical Support Manager
MidNite Solar Inc.
ryan at midnitesolar.com
360-403-7207 XT 151
Skype ID ryan.midnite
On 2/27/2013 11:21 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
We are installing the system today and I only have 60amp in stock. Customer
lives in CA and is leaving today after the installation.
Larry Crutcher
Starlight Solar Power Systems
On Feb 27, 2013, at 9:17 AM, Jonathan Hill wrote:
Why not use one of Midnite's new 100 amp din breakers?
Jonathan Hill
Solar applications engineer
Solar Electric Supply
530-559-3781
solarjon at solarelectricsupply.com
On Feb 27, 2013, at 8:06 AM, "Larry Crutcher, Starlight Solar Power
Systems"<larry at starlightsolar.com> wrote:
Hello Wrenches,
I am installing a Classic 150 controller in an RV with potential 95 amps
output at 12 volts. The customer has a Midnite DIN box and wants me to use
it for the controller output. I am out of 150VDC breakers but I have two 60
amp breakers. Is it safe and reliable to use the 2 breakers in parallel for
this purpose? I can pin the two handles together. There will be other
circuit protection at the battery.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
for the use of the individual or entity who is the intended recipient and
may contain information that is privileged, confidential and exempt from
disclosure or any type of use under applicable law. If the reader of this
e-mail is not the intended recipient, or the employee, agent, or
representative responsible for delivering the e-mail to the intended
recipient, you are hereby notified that any dissemination, distribution,
copying, or other use of this e-mail is strictly prohibited. If you have
received this e-mail in error, please reply immediately to the sender.
P Please think of the environment before printing this email
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.2899 / Virus Database: 2641/6135 - Release Date: 02/26/13
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130227/cc0fcc26/attachment-0003.html>
More information about the RE-wrenches
mailing list