[RE-wrenches] DC circuit breakers in parallel

John Berdner John.Berdner at solaredge.com
Wed Feb 27 11:05:52 PST 2013


Larry:

The Code requires parallel breakers to be designed for this application (internally ganged).
Just using a handle tie does not allow you to use the poles in parallel.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ryan
Sent: Wednesday, February 27, 2013 8:45 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] DC circuit breakers in parallel

Larry
Our 100 amp din rail is essentially 2 breakers in parallel. So in theory the 2 60 amp breakers "Could" work but. My concern would be that they may not be tripped at the same time where they are not internally ganged. I can't say "Go Ahead" but.

Ryan


--

Ryan Stankevitz

Technical Support Manager

MidNite Solar Inc.

ryan at midnitesolar.com<mailto:ryan at midnitesolar.com>

360-403-7207 XT 151

Skype ID ryan.midnite


On 2/27/2013 11:21 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
We are installing the system today and I only have 60amp in stock. Customer lives in CA and is leaving today after the installation.

Larry Crutcher
Starlight Solar Power Systems


On Feb 27, 2013, at 9:17 AM, Jonathan Hill wrote:

Why not use one of Midnite's new 100 amp din breakers?

Jonathan Hill
Solar applications engineer
Solar Electric Supply
530-559-3781
solarjon at solarelectricsupply.com<mailto:solarjon at solarelectricsupply.com>


On Feb 27, 2013, at 8:06 AM, "Larry Crutcher, Starlight Solar Power Systems"<larry at starlightsolar.com<mailto:larry at starlightsolar.com>> wrote:
Hello Wrenches,

I am installing a Classic 150 controller in an RV with potential 95 amps output at 12 volts. The customer has a Midnite DIN box and wants me to use it for the controller output. I am out of 150VDC breakers but I have two 60 amp breakers. Is it safe and reliable to use the 2 breakers in parallel for this purpose? I can pin the two handles together. There will be other circuit protection at the battery.

Thank you,

Larry Crutcher
Starlight Solar Power Systems






_______________________________________________

List sponsored by Home Power magazine



List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>



Change email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org>



CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
P  Please think of the environment before printing this email
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130227/a56af0f5/attachment-0003.html>


More information about the RE-wrenches mailing list