Most structural engineers I've seen take a reduction for slippery surface but I think you'd be stretching things to say adding PV panels reduces the load to zero.  I have a 45 degree pitch roof and I get snow build up some times especially if we get freezing rain before the snow.

Also if you have an asphalt shingle roof you can create an unbalanced load with snow sliding off the south side and sticking on the north side.  Most engineers take this into consideration too.

Thanks,