The idea of the electronics "wearing out"is a strange one. The inverters
are only at full capacity for a small amount of the time, at peak hours
which is only 2 to 4 hours a day, and only for part of that time if you
have clouds, and who doesn't?
Pushing them a little harder should not "wear them out". So one question
would be, what is the rated duty cycle of the inverters?

Let's remember, we are not proposing to increase the operating voltage,
just to provide more current when needed. It's the inverter that chooses to
use the available current.


On Tue, Jan 29, 2013 at 2:21 PM, Great Northern Solar
<gosolar at cheqnet.net>wrote:

> Just to add another $.02:
>
> I agree with Mr. Berdner, wearing out the electronics is a significant
> cost in that scenario.
>
> Energetically,
> Christopher LaForge
> Great Northern Solar
> 77480 Evergreen Road, Suite #1
> Port Wing, WI 54865
> 715 774 3374
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20130129/dadf132a/attachment-0003.html>


More information about the RE-wrenches mailing list