Jesse,

Any metallic raceway that has a GEC running through it needs bonding. So,
if you've got the Enphase DC-GEC running through it then, yes, it would
need bonding fittings. At least that's my take on it.

Check out NEC 250.64(E) towards the second half of the paragraph. 2011 NEC
has a nice clarification point and directs you to 250.92(B)(2) through
(B)(4).

Best,

August


August Goers

Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
m: 415.559.1525
o: 415.641.4000
august at luminalt.com

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Thursday, January 24, 2013 8:45 AM
To: Wrenches
Subject: [RE-wrenches] Bonding bushings?

If you are using micro inverters and terminating them in an AC combiner
panel, does the feed for the AC combiner panel (125A) need to have bonding
bushings for the ground wire?  In other words is this ground wire a
GEC/Equipment ground like might be used if running an inverter output to a
panel?  The raceway is already in and is EMT.

Thanks!

Jesse

Sent from my iPhone
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



More information about the RE-wrenches mailing list