Hi Robert,

Get a mega Ohm meter, isolate the home runs and perform a test.  You should
get >550 MOhms.  If not, there's something likely wrong with that string
that's causing the intermittent ground fault.  Or, have someone stand on
the ground with a hose pointing it at the roof and try to find it using the
voltage method you've been doing.

Date: Mon, 26 Nov 2012 16:55:16 -0800
From: Robert Nuese <robertnuese at sonic.net>
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Unisolar Intermittent Ground Fault
Message-ID: <9C067B77-378B-40ED-AB44-FF966DC20773 at sonic.net>
Content-Type: text/plain; charset="us-ascii"

Dear Wrenches

I've been experiencing a troubleshooting problem that you may be able to
help me with.  Or, can anyone refer me to someone, maybe an electrical
engineer?, who I could hire to help.
nt.
Any recommendations? Probably needs to be someone within 100 miles of
Sebastopol CA.

Thanks,
Robert Nuese