Jason,
The same applies in the CE Code for enclosures/conduit below grade, Šinside
is to be considered 'wet'.

Hope you are able to use this discussion to eliminate the need for the extra
attic jbox.
Benn

DayStar Renewable Energy Inc.
www.daystarsolar.ca  *  Ph: 780-906-7807
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY

On 26/10/12 2:02 PM, "Jason Szumlanski" <jason at fafcosolar.com> wrote:

Benn,

Wet location is defined, but there are also specific elaborations throughout
the code. As an example, for an enclosure mounted below grade, the interior
of the enclosure is also considered to be wet. There is nothing specific in
the code that defines the interior of a junction box mounted in a wet
location as a wet location also. However, that is up the the interpretation
(dare I say whim) of the AHJ. We have been required to use wet location
rated splices and connections inside roof mounted junction boxes by some
inspectors. Using the same logic, NM cable would not be acceptable.

Nonetheless, I think you are correct and on the right track, and I'm going
to give it a whirl.

Jason Szumlanski 

Fafco Solar

On Fri, Oct 26, 2012 at 2:02 PM, benn kilburn <benn at daystarsolar.ca> wrote:
> Glenn/Jason,
> So you wouldn't use romex to feed an exterior outlet on an outside wall, or to
> any outside lights???
> 
> Canadian Electrical Code's (CE Code) definitionsŠ
> wet location -a location in which liquids may drip, splash, or flow on or
> against electrical equipment.
> Damp location ­an exterior or interior location that is normally or
> periodically subject to condensation of moisture in, on, or, adjacent to
> electrical equipment an includes partially protected locations under canopies,
> parquees, roofed open porches, and similar locations.
> Dry location ­a location not normally subject to dampness, but that may
> include a location subject to temporary dampness as in the case of a building
> under construction, provided that ventilation is adequate to prevent an
> accumulation of moisture.
> 
> If inside your attic is considered a "wet location", then you have other
> issues.  Are you sure the NEC's definition of 'wet location' is relating to
> the location of the romex?
> I just spoke to one of my inspectors and he sees no issue with entering the
> bottom of a soladeck with romex.
> 
> On the grounding/bonding, I have been using the bare wire in the romex for the
> enphase system ground (within the enphase cable) and running a #6 from the mod
> frames and rails into the soladeck and along side the romex back to the
> panelboard.
> 
> I need to get myself a copy of your NEC so I can be on the same page as you
> guys.  I hear it is written in a way that is much easier to interpret than the
> CE Code, which is written in a very legal jargon.
> 
> Cheers,
> benn
> DayStar Renewable Energy Inc.
> www.daystarsolar.ca <http://www.daystarsolar.ca>   *  Ph: 780-906-7807
> <tel:780-906-7807>
> Construction Electrician Solar Photovoltaic Systems Certified
> Certificate # 0007S
> HAVE A SUNNY DAY
> 
> On 25/10/12 9:37 AM, "Glenn Burt" <glenn.burt at glbcc.com> wrote:
> 
> Soladeck on the rooftop places it in an environment that is considered Œwet¹.
> I don¹t think Romex is listed for use in a wet environment.
>  
> This would force you to use the proposed jbox in the attic for the transition
> location.
> I also understood that you could combine the EGC and GEC into a single
> conductor as long as it is continuous or irreversibly spliced, as part of the
> ¹08 code.
>  
> -Glenn Burt
>  
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
> Szumlanski
> Sent: Thursday, October 25, 2012 9:13 AM
> To: RE-wrenches
> Subject: [RE-wrenches] Enphase and Romex
>  
> I'm sure this has been covered, but I could not find it in the archives.
> 
>  
> 
> We are considering using Romex in the attic for the first time. My plan was to
> use the new Enphase coupler to connect the trunk cable to Type TC-ER, enter a
> Soladeck passthrough box on the roof into a junction box in the attic where I
> would make the transition to 10/3 Romex. I'm hung up on the GEC going back to
> the service panel. Any suggestions?
> 
>  
> 
> By the way, we are on NEC 2008, and in most cases there is also a requirement
> for an additional grounding electrode per NEC 690.47(D) (that shouldn't really
> relate to my issue).
> 
> Jason Szumlanski 
> 
> Fafco Solar
> _______________________________________________ List sponsored by Home Power
> magazine List Address: RE-wrenches at lists.re-wrenches.org Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules
> & etiquette: www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
> 
> 


_______________________________________________ List sponsored by Home Power
magazine List Address: RE-wrenches at lists.re-wrenches.org Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List
rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant
bios: www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121028/4754fb94/attachment-0004.html>


More information about the RE-wrenches mailing list