We came across an interesting situation in a local winery recently:
The service is 480 volts and the inverters are operating at 208 volts. To
make the two systems connect, the original installer integrated a 480 Delta
to 208 Wye transformer, pretty standard procedure.
We found a stray voltage of 18 volts between the neutral and ground as
measured in the AC combiner panel. I noticed that there was no bond
between the neutral and the ground in this panel. I do not believe this is
correct. One reason is the stray voltage seems wrong. Another, more
important consideration is that I do not believe there is path for fault
currents to return to the transformer. In the case of a phase short to
chassis, there would be no fault current to open the OCPD.
Is my analysis correct here?