Hi Ron,

Its a real bitch to walk someone through the XW control panel.

But I'm guessing that they added something recently , say an Air conditioner?

Default settings are 60 amps, which would put the genny under a world of hurt.

Another thought.

Is the generator in a shed or open?  ie good airflow or not.

another way to really kill them, get them really really hot.

Good luck,

jay

On Aug 16, 2012, at 5:32 PM, Ron @ earthRight Solar wrote:

> Hi Jay,
> 
> Thanks for the suggestions. I'm not big on generators or on Xantrex so may be missing something. It's possible the load on the generator is too high, it's a young family and use lots of power. There is no grid so I'm guessing you mean connected to the wrong input on the XW? So if they connected the generator to the grid input instead of generator input then the PV could be trying to sell back to the generator?? Is this possible?
> 
> It's a first nations group several hours in the back country so not so easy to troubleshoot. 
> 
> Ron
> 
> On 2012-08-16, at 5:24 PM, jay peltz <jay at asis.com> wrote:
> 
>> Hi ron,
>> 
>> Interesting problem.
>> 
>> The XW-AGS is a dry contact system so should be no voltage there, and since that "worked" for years, seems unlikely.
>> 
>> Only thoughts at this point are.
>> 
>> 1. load on genny is too high.
>> 
>> 2. generator is connected to the Grid input and it trying to sell back.
>> 
>> 3.  any new loads or production sources added lately?
>> 
>> 4. Its not the generator, but something outside of it thats changed.
>> 
>> Good luck,
>> 
>> Jay
>> 
>> peltz power
>> 
>> 
>> 
>> 
>> On Aug 16, 2012, at 3:30 PM, Ron @ earthRight Solar wrote:
>> 
>>> Hi Wrenches,
>>> 
>>> I have a client that has burned up two control boards on an Onan-Cummings 5.5 kw propane generator. The system includes an XW 6048 inverter, XW MPPT c.c., and the Onan generator. System has worked well for several years but recently burned up the control board on the Onan. Client decided to purchase a new Onan instead of paying $1k for a new control board. The new Onan lasted one week and the same result, control board fried. He is consulting with me at this point - I didn't supply any of this equpt. - and Onan supplier is being completely unhelpful. I'm trying to do a little detective work here and discover the cause of the problem. I'm wondering if it could be the XW-AGS possibly sending too high voltage to the Onan controller. Has anyone had issues with these? Any suggestions?
>>> 
>>> Ron Young
>>> 
>>> earthRight Products - Solareagle.com
>>> 
>>> Williams Lake, BC
>>> V2G 2A3
>>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120816/7db35a59/attachment-0004.html>


More information about the RE-wrenches mailing list