Dan Fink danbob88 at gmail.com
Thu Mar 29 12:04:16 PDT 2012


Turning on other loads around the shop seems to work here. But we need
to have over 100 watts on (we are using lights) to prevent the
problem. It's a PITA, as it crashes the satellite internet, which
takes 20-60 minutes to boot back up.

DAN FINK

On Thu, Mar 29, 2012 at 12:12 PM,  <penobscotsolar at midmaine.com> wrote:
> We've seen this type of problem twice with well pumps. Both times, the
> problem was with a short in the load side close to the pump. One was
> occasional, the other constant. Interestingly, running a large generator
> seemed to "fix" the situation to the customer. In both cases, we found the
> short, repaired it and both systems are still working well to this day.
> One used a transformer, the other was a single 4024SW.
>
> Daryl
>
>
>
>> Hi Mac;
>>
>> We are having a similar problem at our metal shop with two stacked
>> SW4024s. They are stacked so that inverter #2 idles until something
>> 240V is turned on -- well pump and welder are the only 240 VAC loads.
>> We are getting an overcurrent error and shutdown by just turning the
>> welder's power switch on -- NOT when starting to weld.
>>
>> Any help from the list appreciated!
>>
>> --
>> Dan Fink,
>> Executive Director;
>> Otherpower
>> Buckville Energy Consulting
>> Buckville Publications LLC
>> NABCEP / IREC accredited Continuing Education Providers
>> 970.672.4342 (voicemail)
>>
>> On Thu, Mar 29, 2012 at 8:25 AM, mac Lewis <maclewis1 at gmail.com> wrote:
>>> Hello wrenches,
>>>
>>> I have a customer that I have been working with over the phone.  He has
>>> a SW
>>> 4024, with a T240 transformer feeding a 2 HP well pump on a timer.   The
>>> system has worked well for years, but recently, he has been getting
>>> overcurrent errors when the well pump starts.  It's not every time, but
>>> about every other time.  He also did an experiment where he turned off
>>> the
>>> well pump, and gets the overcurrent error just energizing the
>>> transformer.
>>>  Does this indicate the transformer is failing?  What are other
>>> explanations
>>> for this behavior?
>>>
>>> Thanks for any advice