[RE-wrenches] Apparent power
Darryl Thayer
daryl_solar at yahoo.com
Mon Feb 6 19:01:08 PST 2012
The first thought that comes to mind is recative power is not real power, and is normally solved with pavsive devices like capacitor banks. There are things like switchable capacator banks that canvary the reactive power by having diffreent amount of capacators to the line.
So although I think inverters can reactive correction, why not use a capacitive device?
Darryl
________________________________
From: "boB at midnitesolar.com" <boB at midnitesolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Saturday, February 4, 2012 8:05 PM
Subject: Re: [RE-wrenches] Apparent power
Sounds like a voltage source (and sinking) inverter to me.
These types can cause current distortion which the UL1741 / IEEE
1547 specs try to prevent.
Apparent must be able to turn that mode on and off I would
imagine. It's not too difficult to do. No wonder
they talk about micro-grids.
The old Trace SW series was a voltage source inverter, even when
grid tied and is basically why they had
to add that extra inductor box between SW and the grid when selling.
It could actually help the grid wave-
form voltage if it was distorted because of non-linear loads.
boB
On 2/4/2012 5:26 PM, Comet Systems wrote:
As I understand the issue they claim to be able to address, the utilities often need a source of reactive power close at the system delivery points, the customer sites, because reactive power does not transmit well through the lines and transformers and uses up transmission resources better used for real power. The reactive power is used as a method of voltage control.
>Therefore, it is reasonable that the utilities would pay a premium for a reactive power source which would be close to the customers and under their control. The idea has some merit and could be a significant direction for solar pv, but whether an electronic inverter can adequately generate reactive power at will, to act as a compensation device and whether that is the highest and best use for that power source is to be demonstrated. Interesting idea, though.
--
>Chris Mason
>President, Comet Systems Ltd
>
>
>
>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120206/85e6b5c1/attachment-0004.html>
More information about the RE-wrenches
mailing list