[RE-wrenches] Generator Selection -- XW specific
Maverick Brown [Maverick Solar]
maverick at mavericksolar.com
Mon Jan 16 13:58:47 PST 2012
I was able to edit two parameters guided by Xantrex to make the issue go
away. You will need the Xantrex Configuration Tool and the tech note /
software tool from Xantrex. But otherwise its pretty simple to do. Of
course, a firmware update will make the incompatibility go away easier.
Software upgradeability is a great feature on inverters.
Thanks
Maverick
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, January 16, 2012 2:52 PM
To: RE-wrenches
Subject: [RE-wrenches] Generator Selection -- XW specific
Friends:
The Kohler RES series generator has a bug when used in conjunction with the
Xantrex XW inverters: The power waveform of the RES generators is distorted
under no-load conditions. The result is that the XW will not connect. A
fix is pending but a new firmware release date is not yet predicted.
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list