Mac:
Nope.
William Miller
PS: It's pretty straight forwards, the code says "bus or conductor."
wm
PPS:
Can you customer live with a smaller feeder breaker, say 125 amps? If so,
your gold.
wm
At 06:43 PM 9/27/2012, you wrote:
>Hello wrenches,
>
>I am looking for advice on how the 120% rule applies to feeders for a
>subpanel. I have this scenario:
>150A bus rating on subpanel with main breaker of 100A. The conductors
>feeding this subpanel are 100A rated conductors. Can I backfeed with a
>40A breaker?
>
>Thanks
>
>--
>
>
>
>Mac Lewis
>
>"Yo solo sé que no sé nada." -Sócrates
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>Internal Virus Database is out of date.
>Checked by AVG - www.avg.com
>Version: 8.5.455 / Virus Database: 271.1.1/5272 - Release Date: 09/16/12
>18:34:00
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120927/fab220ac/attachment-0003.html>
More information about the RE-wrenches
mailing list