[RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

Kent Osterberg kent at coveoregon.com
Fri Sep 14 17:00:21 PDT 2012


See 690.13. There must be a means to disconnect all conductors of a PV 
system. If it is a normally grounded array you are not allowed to put a 
switch in the grounded conductor, except .... for circumstances added in 
the 2011 code.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 9/14/2012 4:39 PM, Bob Clark wrote:
>
> Wrenches:
>
> A local utility person has suggested that both the positive and 
> negative conductors from a solar array should be disconnected.
>
> Disconnect both or not?  2008 NEC supporting citation please.
>
> Thanks for your response.
>
> *Bob Clark*
>
> */SolarWind Energy Systems, LLC/*
>
> *P.O. Box 1234*
>
> *Okanogan, WA 98840*
>
> *(509) 826-1259*
>
> **
>
> /Although no trees were killed in the sending of this message, a large 
> number of electrons were terribly inconvenienced./
>
> cid:822514723 at 19022009-0502
>
> *//*
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120914/95c938c8/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 5184 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120914/95c938c8/attachment-0006.png>


More information about the RE-wrenches mailing list