[RE-wrenches] Ilsco SGB bonding lug
benn kilburn
benn at daystarsolar.ca
Mon Aug 27 16:11:00 PDT 2012
Thanks for the feedback Wrenches, lots of interesting comments,
However I'm still wondering..
How does one confirm that it is specifically approved for outdoor use?
Other than assuming it is implied (because it is 'marketed' as a solar lug).
As far as I can tell UL 467 does not imply "outdoor rated" as the aluminum
lug "GBL-4" is also UL467 listed. See hereGBL LAY-IN AL/CU
<http://ilsco.com//ProductsDetail.aspx?kfjkff=cjiDRFP14PUgtVid3pn1cQ%3d%3d&f
jjfhjhj=nY1wgyVO%2fE%2bFsQNfsmn%2f4OZ3BP5vHo5NcMahtvvHLIc%3d> .
As well, and as Gary pointed out with his second link, for a module
bonding/grounding method to be acceptable, it must be recognized by the
module manufacturer, no?
Which means that any new bonding product on the market must have the
blessing of each mod mfgr.
(by way of letter or mention in its install manual). I have come across
inspectors that actually look for this.
Jason,
you wrote "I like the looks of that lug. However, I've been using WEEBs too
long to go back now." I agree, and i'm not looking to replace weebs with
these, but these certainly seem to have a place in the What do you use for
the bonding connection from the ?rails?
This SGB lug was suggested for this purpose as well.
Benn
DayStar Renewable Energy Inc.
www.daystarsolar.ca * Ph: 780-906-7807
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY
On 27/08/12 2:35 PM, "Gary Willett" <gary at icarussolarservices.com> wrote:
Here's the Ilsco listing from UL, where it's classed as "Grounding and
Bonding Equipment":
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name
=KDER.E34440&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074099002&
cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
The GuideInfo for Grounding & Bonding Equipment lists:
> Grounding and Bonding for Photovoltaic (PV) Systems Grounding and bonding
> equipment intended for use in PV systems are additionally investigated in
> combination with the PV module/panel (see QIGU) to the applicable requirements
> for such products. Installation instructions provided with the PV system (see
> QIGU) identify the specific grounding and bonding device that has been
> investigated and intended for use with that system.
>
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&na
me=KDER.GuideInfo&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=107409
8839&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
Regards,
Gary Willett, PE
On 8/27/2012 3:20 PM, David Brearley wrote:
> Yes, sorry. I wasn't speaking of this lug...I like the redesign. Looks quicker
> and easier and robust.
>
>
>
> On Aug 27, 2012, at 3:17 PM, Jason Szumlanski wrote:
>
>
>> Yeah, but this one is marketed as a solar bonding lug. I think it's safe to
>> say that it appropriately rated for outdoor use. It's always good to
>> double-check, of course.
>>
>> Jason Szumlanski
>> Fafco Solar
>>
>>
>>
>>
>>
>>
>> On Mon, Aug 27, 2012 at 4:11 PM, David Brearley
>> <david.brearley at solarprofessional.com> wrote:
>>
>>>
>>> Some of the aluminum lugs are indoor-rated. They have a set screw will rust
>>> in an outdoor environment. That's one of the classic John Wiles slides. I'd
>>> just watch out for that....
>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> On Aug 27, 2012, at 12:53 PM, Brian Mehalic <brian at solarenergy.org> wrote:
>>>>
>>>>
>>>>
>>>>>
>>>>> I believe the UL467 listing means that it is rated for direct
>>>>> burial/outdoor use.
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> Brian Mehalic
>>>>> NABCEP Certified Solar PV Installer R031508-59
>>>>> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> PV Curriculum Developer and Instructor
>>>>> Solar Energy International
>>>>> http://www.solarenergy.org <http://www.solarenergy.org/>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>
>>>>>
>>>>> .org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120827/79ca6a02/attachment-0003.html>
More information about the RE-wrenches
mailing list