[RE-wrenches] Heart Interface Inverter

Jay Peltz jay at asis.com
Sat Aug 18 07:23:40 PDT 2012


Hi folks
You might also check peak volts. If memory serves correctly those  older inverters charged off peak volts not RMS. 

Jay
Peltz power

Sent from my iPhone

On Aug 18, 2012, at 7:07 AM, "bob ellison" <reellison at gmail.com> wrote:

> Try putting a load on the generator (like a 1500 watt hair dryer) before the Heart kicks on then once it transfers to the loads and starts charging, shut it off.
> It might be finding the voltage or frequency to high for it’s liking.
> Plug it directly into the generator of somewhere before the inverter to get gen power.
>  
> Bob Ellison
>  
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Mason
> Sent: Saturday, August 18, 2012 7:26 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Heart Interface Inverter
>  
> For what it's worth, the Fluke is known to mistake harmonics for base frequency. I would look to borrow for a scope or at least use a cheaper meter that can accurately report the frequency. Try slowing the generator to 59 Hz to see if the inverter likes it better.
> 