[RE-wrenches] 12V loads

Drake drake.chamberlin at redwoodalliance.org
Sat Aug 11 05:43:29 PDT 2012


Ray,

If golf cart batteries can't surge over 2000 amps, then it would seem 
that the fuse in line with the QO can be deleted in some cases.  Is 
the 2000 A surge for one 6 volt battery or 2 in series?

Fuses can be put in the QO enclosure ahead of the loads and DC rated 
Class T fuses can be bolted to battery terminals (code questionable, 
but a good method for safety).  In the old days we often had a DC 
system with a few lights and maybe a Sunfrost.  That way, if the 
inverter went down, the home wouldn't be left in the dark. DC was 
tricky code wise, but not impossible.

Thanks

Drake


At 08:03 PM 8/10/2012, you wrote:
>The QO breaker has an AIC of 5000 amps.  The usual golf cart 
>batteries have a short circuit current of about 2000 amps, so you 
>could do a set of 4 golf cart batteries at 12v, without worrying 
>about the extra fuse.
>Once again, if the system gets any bigger, they should just go to an 
>inverter based design.
>Also, to be clear, I don't risk my license installing ATC fused 
>systems on permanent structures.  (strictly RVs, and portable set ups)
>As soon as I'm doing an install covered by the code, it's going to 
>be code compliant, and it's going to be inverter based.
>Take a look at Midnite's Mini DC panel wired to Magnum's smallest 
>inverter.  You'd be surprised how cheap you can do a code compliant 
>inverter based system, and how much money you can waste trying to do 
>a code compliant DC only system.
>
>Ray Walters
>NABCEP certified since 2004
>
>On Aug 10, 2012, at 4:35 PM, Drake wrote:
>
> > I second using QO load centers.  You will want to put a fuse, 
> like an FRN-R, between the battery and the load center, as the QO 
> breakers don't have a high AIC rating. 12 V systems can be wired as 
> easily as a regular AC system.
> >
> >
> > At 05:05 PM 8/9/2012, you wrote:
> >> Hello,
> >>
> >> I've been looking at a lot of hunting shacks, fish houses and 
> other 12V loads setups and was wondering how people go about 
> setting these up? What are people using for load termination, fusing?
> >>
> >> I'd like to keep all disconnects and fusing in one "box".
> >>
> >> Jesse
> >>
> >> Sent from my iPhone
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org




More information about the RE-wrenches mailing list