[RE-wrenches] Smart grid grid-connected compatibility
Kent Osterberg
kent at coveoregon.com
Sun Jul 8 16:06:06 PDT 2012
Wrenches,
There weren't very many replies to my question about grid-connected
inverter compatibility with utility remote meter reading systems so I'll
explain my recent experience with hope that this information may be of
assistance sometime.
Last fall I installed an Ephase system for a customer. Soon after it was
on line he complained that the inverters were dropping off line
frequently. Since we had a lot of cloudy weather in northeast Oregon all
winter, it wasn't easy to see what was going on. In the spring we had
some clear days and noticed that the inverters were dropping off line
several times a day at exactly the same time every day. It didn't take
very long for our suspicion to turn to the utilities new remote meter
reading equipment. Because our weather has been so cloudy it took a
while to find clear days where the utility could provide assistance. But
with their help by reading the meter on demand and temporarily disabling
the meter communications we were able to finally prove the remote meter
reading system is tripping the inverters offline for five minutes every
time the meter sends a data packet.
Recently the remote meter reading system has expanded to more areas so
we have now observed this problem with both Enphase M190 and M215
inverters. The system we've observed that is in town is seeing many more
dropouts, so we think every kWh meter on the same service transformer
and maybe some beyond it are causing trouble too.
The remote meter reading equipment is made by Aclara and uses their
TWACS technology. This isn't new technology and with more remote meter
reading systems going in all the time there will be more occurrences of
incompatibility. Certainly more between Enphase and TWACS. And possibly
more between other inverters and other communications systems.
At present I'm really dissatisfied with Enphase's support on this issue.
All they've done is point out that only a few systems have been affected
and put us in the position of telling customers that they'll just have
to live with the lost production time. Until Enphase comes up with a
fix, I won't install any more Enphase inverters.
--
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882
More information about the RE-wrenches
mailing list