I've seen batteries get very hot from deficit
charging, where batteries are cycled rapidly and never fully charged.
At 10:15 PM 4/12/2012, you wrote:
>I have seen very hot batteries infact batteries
>that melted. and caught fire. the problem was
>that the string was several strings in parallel,
>and one of the strings had thermal
>runaway. during charge one battery got hot, and
>it has lower voltage and gets more current. then
>it get hotter because of the more curent. soon
>it is so hot the other batteries start to discharge through the hot battery.
>
>A similar event will occur when one battery in a
>string of batteries develops a bad cell, and the
>othe batteries in parallel strings will force
>current backwards through the cell. and thermal
>runaway occcurs in the hot battery.
>
>From: Jason Szumlanski <jason at fafcosolar.com>
>To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>Sent: Monday, April 2, 2012 11:53 AM
>Subject: Re: [RE-wrenches] Hot Trojan Batteries
>
>There must be some confusion here about the
>charging rate. C/20 refers to capacity divided
>by 20, so in the case of a 325aH battery
>(capacity @ the 20 hour discharge rate) weâre
>talking about charging at a 16.25 amp rate.
>Iâm sure John is not referring to a maximum
>rate of 10-15% of 16.25 amps, but 10-15% of the 325aH capacity.
>
>Jason Szumlanski
>Fafco Solar
>
>
>From:
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John DeBoever
>Sent: Monday, April 02, 2012 12:14 PM
>To: <mailto:allsolar at scswifi.net>allsolar at scswifi.net; RE-wrenches
>Subject: Re: [RE-wrenches] Hot Trojan Batteries
>
>Jeremy, Wrenches,
>
>165°F is definitely too high and you should
>stop immediately any charge to avoid further
>major problems. I recommend you contact our
>Trojan Tech Support for help at
>http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
>
>
>Below are few perspectives to help the diagnostic:
>
>o System issues:
>ü Check Charger setting: the C/20 rate
>mentioned is definitely too high and will damage
>the battery. The maximum recommended current
>rate is 10-15% of C/20 for a deep-cycle flooded
>lead acid battery. Other C/rates are possible
>but are application specific and not typical.
>ü Check Voltage settings: these are provided
>on Trojan datasheets, see here:
>http://www.trojanbatteryre.com/Tech_Support/literature.html
>ü Check Temperature compensation: -0.028VPC
>for every 10°F above 77°F (add 0.028 VPC for
>every 10°F below 77°F or subtract 0.020VPC for
>every 10°F above 77°F. See here:
>http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf
>ü Check Voltage sensor status and connection.
>Dedicated wiring is recommended
>ü Check temperature sensor. It shall be well
>positioned, typically in the middle of the battery bank at the warmest point.
>ü Check if air circulation between the battery units.
>ü Check if adequate air ventilation of the battery room.
>
>o Battery issues:
>ü C/20 charging rate is too high (see above)
>ü How old are the batteries? Ageing batteries
>will face micro-shorts that will decrease the
>battery turnaround efficiency over time that
>translates in higher temperature generation.
>Typically the battery temperature range is about
>20oF above ambient temperature, and typical min
>and max limit are -4°F to 113°F.
>See here:
><http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf>http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf
>
>165°F is way too high and will damage the units
>ü Maybe you are facing one or more shorted
>units: check the voltage and it will quickly
>indicate if a unit is shorted. Shorted units
>will generate heat and will jeopardize the
>charging of other units. Remove shorted units
>and consult tech support your charger supplier
>if possible to reconfigure of your battery bank
>with fewer units, configured at a lower battery
>bank voltage, using same voltage settings
>recommended by Trojan Battery
>Company. Typically 1 to 3 units less would be
>acceptable, depending the charger manufacturer settings.
>ü Maybe you are facing sulfated batteries,
>resulting from low charging, thus resulting in
>lower overall turnaround efficiency. This will
>heat some healthier units of the battery bank,
>accelerating corrosion damages. The max
>temperature acceptable being 113°F, please
>consult Trojan Tech Support:
><http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top>http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
>ü Please deal directly off-Wrenches list, with
>Trojan Tech Support for better fine tune
>resolution:
><http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top>http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
>
>I hope this help,
>
>John
>John F. DeBoever
>Global Technical Director Renewable Energy
>Trojan Battery Company
>
>12380 Clark Street
>Santa Fe Springs, CA 90670
>Tel: +1-562-236-3000 Ext. 3139
>Cell: +1-845-514-7600 NY office time zone: USA EST (GMT-5)<
>Skype: john.f.deboever
>Fax: +1-562-236-3239
><mailto:jdeboever at trojanbattery.com>jdeboever at trojanbattery.com
>www.trojanbattery.com
>
>-----Original Message-----
>From:
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org]
>On Behalf Of <mailto:allsolar at scswifi.net>allsolar at scswifi.net
>Sent: Sunday, April 01, 2012 7:20 PM
>To:
><mailto:re-wrenches at lists.re-wrenches.org>re-wrenches at lists.re-wrenches.org
>Subject: [RE-wrenches] Hot Trojan Batteries
>
>Wrenches,
>Can anyone explain why an L16 bank would be at
>165F at rest. Over a C20 charge rate, but I
>have a feeling there might be an internal short
>
>Jeremy
>All Solar
>Sent via BlackBerry. Sorry for typos and shorthand!
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>This e-mail message and any attachments that
>accompany it may contain information that is
>confidential, privileged, or protected from
>disclosure. It is intended solely for the use of
>the individual(s) to whom it was intended to be
>addressed. If you have received this e-mail by
>mistake, or you are not the intended recipient,
>any reading, disclosure, copying or other use of
>this communication is strictly prohibited. If
>you have received this communication in error,
>please immediately advise the sender at their
>phone number listed above, or by electronic
>mail, and also permanently delete the original
>and all copies of this e-mail and any
>attachments from all locations. Thank you.
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120413/7acada74/attachment-0003.html>
More information about the RE-wrenches
mailing list