[RE-wrenches] Charge Rate (Hot Trojan Batteries)

All Solar, Inc. allsolar at scswifi.net
Tue Apr 3 07:24:16 PDT 2012


With 5 strings installed, I figured the charge rate to be about 3.3% (of C20 rate) for 5 years or so. Actually since it was installed in 2002, and now on its second set of batteries.  
We added some PV and an MX60 a year ago, and now this.  I think he had heavily sulfated batteries which eventually led to shorted cells. ?
Jeremy 
  ----- Original Message ----- 
  From: Jason Szumlanski 
  To: RE-wrenches 
  Sent: Monday, April 02, 2012 1:43 PM
  Subject: Re: [RE-wrenches] Hot Trojan Batteries


  There are a lot of forums and circles where C/20 refers to the capacity divided by 20, or 5% of the battery capacity. This may be the more informal interpretation of the term, but you will find many examples where people consider C/20 to be 5% of the capacity (wrong or right). For example, look at the most frequently accessed deep cycle charging FAQ on the Internet: http://www.windsun.com/Batteries/Battery_FAQ.htm



  To be clear perhaps we should just use plain English and say “the recommended charging rate is 10-15% of the capacity of the battery at the 20 hour discharge rate.”



  Jason Szumlanski

  Fafco Solar





  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
  Sent: Monday, April 02, 2012 1:46 PM
  To: re-wrenches at lists.re-wrenches.org
  Subject: Re: [RE-wrenches] Hot Trojan Batteries



  Wrenches,
  I attended John DeBoever's Friday afternoon presentation on battery technology and care at the NABCEP Continuing Education conference this past weekend. It quickly became clear to me that John seriously knows his batteries, at all levels: chemistry, physics, RE use and care, etc. It was an advanced-level presentation, and I learned a lot. 

  The first thing John told us was that English is not his native language; he's a Belgian raised in South Africa (and more that I didn't catch). He was bursting with knowledge and good information, but occasionally we in his class would back him up to better explain a point. 

  In short, I think he will be a real asset to the Wrenches list as a manufacturer's representative. And occasionally there will be something confusing, such as what just happened here. I too wondered about C20 versus C/20. I appreciate that he quickly cleared up the confusion, and look forward to learning quite a bit from his posts about battery issues.
  Allan

  Allan Sindelar
  Allan at positiveenergysolar.com
  NABCEP Certified Photovoltaic Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Positive Energy, Inc.
  3201 Calle Marie
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com 






  On 4/2/2012 11:00 AM, John DeBoever wrote: 

  Jason, Wrenches,



  C/20 means C over 20 hours discharge rate = capacity @ the 20 hours discharge rate. C/20 often is mentioned as C20, so the confusion here. 

  Max recommended is 10& to 15% of C20 of the battery bank.



  John 

  Trojan Battery Company



  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason Szumlanski
  Sent: Monday, April 02, 2012 12:53 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Hot Trojan Batteries



  There must be some confusion here about the charging rate. C/20 refers to capacity divided by 20, so in the case of a 325aH battery (capacity @ the 20 hour discharge rate) we’re talking about charging at a 16.25 amp rate. I’m sure John is not referring to a maximum rate of 10-15% of 16.25 amps, but 10-15% of the 325aH capacity.



  Jason Szumlanski

  Fafco Solar





  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John DeBoever
  Sent: Monday, April 02, 2012 12:14 PM
  To: allsolar at scswifi.net; RE-wrenches
  Subject: Re: [RE-wrenches] Hot Trojan Batteries



  Jeremy, Wrenches,



  165°F is definitely too high and you should stop immediately any charge to avoid further major problems. I recommend you contact our Trojan Tech Support for help at http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top 



  Below are few perspectives to help the diagnostic:



  o   System issues: 

  ü  Check Charger setting: the C/20 rate mentioned is definitely too high and will damage the battery. The maximum recommended current rate is 10-15% of C/20 for a deep-cycle flooded lead acid battery. Other C/rates are possible but are application specific and not typical.

  ü  Check Voltage settings: these are provided on Trojan datasheets, see here: http://www.trojanbatteryre.com/Tech_Support/literature.html 

  ü  Check Temperature compensation: -0.028VPC for every 10°F above 77°F (add 0.028 VPC for every 10°F below 77°F or subtract 0.020VPC for every 10°F above 77°F. See here: http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf 

  ü  Check Voltage sensor status and connection. Dedicated wiring is recommended

  ü  Check temperature sensor. It shall be well positioned, typically in the middle of the battery bank at the warmest point.

  ü  Check if air circulation between the battery units. 

  ü  Check if adequate air ventilation of the battery room.



  o   Battery issues:

  ü  C/20 charging rate is too high (see above)

  ü  How old are the batteries? Ageing batteries will face micro-shorts that will decrease the battery turnaround efficiency over time that translates in higher temperature generation. Typically the battery temperature range is about 20oF above ambient temperature, and typical min and max limit are -4°F to 113°F. 

  See here: http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf 

  165°F is way too high and will damage the units

  ü  Maybe you are facing one or more shorted units: check the voltage and it will quickly indicate if a unit is shorted.  Shorted units will generate heat and will jeopardize the charging of other units. Remove shorted units and consult tech support your charger supplier if possible to reconfigure of your battery bank with fewer units, configured at a lower battery bank voltage, using same voltage settings recommended by Trojan Battery Company.  Typically 1 to 3 units less would be acceptable, depending the charger manufacturer settings.

  ü  Maybe you are facing sulfated batteries, resulting from low charging, thus resulting in lower overall turnaround efficiency. This will heat some healthier units of the battery bank, accelerating corrosion damages. The max temperature acceptable being 113°F, please consult Trojan Tech Support: http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top

  ü  Please deal directly off-Wrenches list, with Trojan Tech Support for better fine tune resolution: http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top



  I hope this help,



  John

  John F. DeBoever

  Global Technical Director – Renewable Energy

  Trojan Battery Company



  12380 Clark Street 

  Santa Fe Springs, CA 90670

  Tel: +1-562-236-3000 Ext. 3139

  Cell: +1-845-514-7600 – NY office time zone: USA EST (GMT-5)

  Skype: john.f.deboever

  Fax: +1-562-236-3239

  jdeboever at trojanbattery.com

  www.trojanbattery.com



  -----Original Message-----
  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of allsolar at scswifi.net
  Sent: Sunday, April 01, 2012 7:20 PM
  To: re-wrenches at lists.re-wrenches.org
  Subject: [RE-wrenches] Hot Trojan Batteries



  Wrenches,

  Can anyone explain why an L16 bank would be at 165F at rest.  Over a C20 charge rate, but I have a feeling there might be an internal short 



  Jeremy

  All Solar

  Sent via BlackBerry. Sorry for typos and shorthand!

  _______________________________________________

  List sponsored by Home Power magazine



  List Address: RE-wrenches at lists.re-wrenches.org



  Options & settings:

  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



  List rules & etiquette:

  www.re-wrenches.org/etiquette.htm



  Check out participant bios:

  www.members.re-wrenches.org






  This e-mail message and any attachments that accompany it may contain information that is confidential, privileged, or protected from disclosure. It is intended solely for the use of the individual(s) to whom it was intended to be addressed. If you have received this e-mail by mistake, or you are not the intended recipient, any reading, disclosure, copying or other use of this communication is strictly prohibited. If you have received this communication in error, please immediately advise the sender at their phone number listed above, or by electronic mail, and also permanently delete the original and all copies of this e-mail and any attachments from all locations. Thank you. 


  This e-mail message and any attachments that accompany it may contain information that is confidential, privileged, or protected from disclosure. It is intended solely for the use of the individual(s) to whom it was intended to be addressed. If you have received this e-mail by mistake, or you are not the intended recipient, any reading, disclosure, copying or other use of this communication is strictly prohibited. If you have received this communication in error, please immediately advise the sender at their phone number listed above, or by electronic mail, and also permanently delete the original and all copies of this e-mail and any attachments from all locations. Thank you. 

  _______________________________________________List sponsored by Home Power magazine List Address: RE-wrenches at lists.re-wrenches.org Options & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette:www.re-wrenches.org/etiquette.htm Check out participant bios:www.members.re-wrenches.org 

------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches at lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120403/d35cfb57/attachment-0003.html>


More information about the RE-wrenches mailing list