[RE-wrenches] WOW Something Gone Very Wrong
David Brearley
david.brearley at solarprofessional.com
Thu Mar 29 12:41:25 PDT 2012
That was my suspicion as well. Simple wiring mistake. Inadequate
commissioning protocol.
On 3/29/12 2:02 PM, "Bill Brooks" <billbrooks7 at yahoo.com> wrote:
> All,
>
> It is very likely that the something gone very wrong was a wiring mistake by
> the installing contractor. Many installers are clueless about the danger and
> consequences of getting the polarity wrong in strings or combiner box
> circuits. It is very likely that the contractor mixed up their combiner box
> circuits causing the combiner boxes and conductors to catch on fire as soon as
> the fuses were installed.
>
> Polarity should be checked and verified on all circuits a total of 2 or 3
> times during the course of installation and commissioning. It is the single
> most important test from a safety point of view.
>
> Bill.
>
>
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of David Brearley
> Sent: Thursday, March 29, 2012 8:25 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] WOW Something Gone Very Wrong
>
> Perfect example of why it¹s a good idea to start designing and deploying
> systems now that meet the fuse servicing requirements found in NEC 2011even
> if these are not required by your AHJ yet.
>
> People on this list are probably ahead of that curve. If not, you might want
> to check out these articles:
>
> http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2&search= (Bill
> Brooks article on Fuse Servicing disconnect requirements)
>
> http://solarprofessional.com/article/?file=SP4_3_pg64_Hren&search= (Changes
> to Code in 2011; See content under ³690.6, Fuses² subheading)
>
> David Brearley, Senior Technical Editor
> SolarPro magazine
> NABCEP Certified PV Installer
>
> On 3/29/12 9:36 AM, "Mark Frye" <markf at berkeleysolar.com> wrote:
>
>
>
>
> Rooftop solar installation sparks fires in Trenton, New Jersey 28.03.2012:
> According to local news portal NJ.com, a rooftop solar system has triggered
> several small fires at a recycling center in Trenton, New Jersey. The article
> reports that ³a major malfunction in the rooftop solar panelcaused small
> fires and surges of electricity producing arcs of current to break out.²
> According to Fire Battalion Chief Rich Seeds, ³There definitely was a problem
> with the installation, the equipment.² Firefighters on the scene said that an
> inverter was ³sparking and unusable.² The firefighters, with the help of
> electricians, had to manually disconnect the 100-panel system from the
> electrical grid before they could safely put out the fire. The fire started
> while electricians were hooking up junction boxes on the system. Earlier this
> month, a New Jersey General Assembly committee approved a bill (A266) that
> would require buildings to clearly label with an exterior emblem whether they
> have solar panels installed on the premises. The measure, recommended by the
> National Fire Protection Association, is aimed at protecting firefighters from
> dangers posed by solar panels. The greater Assembly has yet to discuss the
> bill, but the New Jersey Senate version of the bill (S507) was introduced in
> the Senate on Jan. 10, 2012 and is currently being reviewed by the Senate
> Environment and Energy Committee. Source: NJ.com, New Jersey Assembly
> Republicans, eLobbyist; Summary: PHOTON
>
> http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle
> _ro.html
> <http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle_ro.htm
> l>
>
>
> http://www.njassemblyrepublicans.com/?p=2862
> <http://www.njassemblyrepublicans.com/?p=2862>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> David Brearley, Senior Technical Editor
> SolarPro magazine
> NABCEP Certified PV Installer
> david.brearley at solarprofessional.com
> Direct: 541.261.6545
> Fax: 541.512.0343
>
> Visit our Web site at solarprofessional.com
>
> (Sample copy available for download at: solarprofessional.com/sample)
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120329/25eae258/attachment-0003.html>
More information about the RE-wrenches
mailing list