Brian,

Would this also work for the Splendide washers? If not, have you come up with any solution yet?

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103



On Mar 27, 2012, at 2:04 PM, Brian Faley wrote:

Hi Kris,
 
A solution to try would be to add a motor run capacitor across the line at the boiler.  10uF-20uf range may improve the crossover distortion enough to allow the boiler ignitor to operate properly. Start with 10uF.
 
Regards,
Brian
 
Brian Faley
Chief Engineer
Magnum Energy Inc.
2211 West Casino Rd
Everett, WA 98204
Ph 425-353-8833
www.magnumenergy.com
 