[RE-wrenches] Metering a whole house Outback system
Hilton Dier III
hiltondier at gmail.com
Mon Aug 20 09:15:59 PDT 2012
Hello Wrenches,
Here's a metering conundrum for you.
I have a client with a dual stacked Outback 3648 inverter panel and a PV
array. He has been off-grid for years, but he is now going on-grid. He
is getting the Outbacks rebuilt at the factory to be grid tie compatible.
As per our local requirements, he needs a meter to read just the output
of the inverter. The problem is that he has the whole house on the
inverters, not just a vital loads panel. He wants to keep it that way.
That gives him two separate outputs, "AC Out" to the main breaker panel
and "AC In(teractive)" to the grid connection. If he just puts a meter
on the AC In line, he will lose track of the inverter output that goes
to power the house, and he'll get his output reduced by any grid-based
charging he does.
There is a "green tag" method of wiring the meter to avoid this, but it
is designed for two single-leg 120VAC outputs and the stacked Outbacks
are putting out 240VAC on two legs.
Aside from dropping $600 on an e-Gauge, is there any way to get around this?
Many thanks,
Hilton
--