[RE-wrenches] Troubleshooting Off-grid PV

Eric Stikes eric at harvesthesun.com
Sun May 27 14:50:48 PDT 2012


Hi Wrenches,

I inherited an off-grid PV system that seems to be significantly under
producing. I have:

12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated
on new 15A breakers in a new Midnite combiner,
Output of combiner passes through a 60A breaker then into a SolarBoost 50
charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a
Yuasa 24V battery bank.

My problem is that I never see more than about 5A (displayed at charge
controller) coming off the array, even in full sun, regardless of the state
of charge of the batteries. I figure I should see, at least once in a
while, closer to between 20-30A. Batteries are, admittedly, passed their
life expectancy as the system was installed in '02 and I am sure this is
part of the problem. I'm thinking that if the batteries are at about 1/2
capacity (don't own a hydrometer...yet), the controller senses the
batteries are near full SOC even at lower voltage (~24V) and is therefore
attempting to trickle charge even in the bulk stage. Though this is not how
the CC is supposed to function in bulk, obviously, I'm assuming the old
batteries are altering the standard operating conditions of the system.
I've adjusted the Bulk set point on the CC but that doesn't seem to make a
difference.

I doubt this is part of the problem but the generator is problematic as
well (it has it's own array of maladies).

Any insight is greatly appreciated. Thanks!

-- 
Eric Stikes
Owner
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com