[RE-wrenches] Heart Interface Inverter

mac Lewis maclewis1 at gmail.com
Thu Oct 11 04:04:18 PDT 2012


Hello wrenches,

Its been a while since I posed a question about this, but I thought I'd
follow up.  I got a chance to get a scope on the propane generator output.
 The voltage output of the propane generator has a significant "bite" out
of the top of the voltage peak.  Jay, I think you were right, the rms
voltage was good, but the peak didn't match up with what the Heart inverter
wanted to see.

Does anyone know what may cause a "bite" in the top of the voltage waveform
of a generator?

Thanks

On Sat, Aug 18, 2012 at 8:23 AM, Jay Peltz <jay at asis.com> wrote:

> Hi folks
> You might also check peak volts. If memory serves correctly those  older
> inverters charged off peak volts not RMS.
>
> Jay
> Peltz power
>
> Sent from my iPhone
>
> On Aug 18, 2012, at 7:07 AM, "bob ellison" <reellison at gmail.com> wrote:
>
> Try putting a load on the generator (like a 1500 watt hair dryer) before
> the Heart kicks on then once it transfers to the loads and starts charging,
> shut it off.****
>
> It might be finding the voltage or frequency to high for it’s liking.****
>
> Plug it directly into the generator of somewhere before the inverter to
> get gen power.****
>
> ** **
>
> Bob Ellison****
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Chris Mason
> *Sent:* Saturday, August 18, 2012 7:26 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Heart Interface Inverter****
>
> ** **
>
> For what it's worth, the Fluke is known to mistake harmonics for base
> frequency. I would look to borrow for a scope or at least use a cheaper
> meter that can accurately report the frequency. Try slowing the generator
> to 59 Hz to see if the inverter likes it better.****
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 



Mac Lewis

*