[RE-wrenches] Automatic Meter Reading WAS: Fronius State 104
Bill Loesch
solar1online at charter.net
Tue Oct 9 06:06:37 PDT 2012
Hi Fellow Wrenches,
Thanks for the insight that AMR systems could interfere with not only
data monitoring (previous thread) but also with the inverter control
function, too.
I have attempted to gain some insight into the AMR system the local
utility uses (Cellnet) but talking to the utility people, they would
have you believe this is privileged if not secret info. When Ameren
first implemented the system (reportedly the largest AMR system in the
nation) they advertized that they would know within seven seconds that
you were without power. That number has been seriously revised upwards
in the interim.
Anyone have any info about using/accessing the AMR info for the customer
to view?
As always, TIA for the collective wisdom,
Bill Loesch
Solar 1 - Saint Louis Solar
On 09-Oct-12 7:06 AM, Jeff Wongstrom wrote:
> All,
>
> The utility(Flathead Electric Co-op) has recently completed automatic
> meter reading using a power line carrier for all co-op members. I
> will give them a call to find out the type and frequency of signaling.
> The state 104 has been occurring within 10 minutes of connecting to
> the grid. Perhaps the IG uses the zero crossing and is confused by
> the meter reading signal.
>
> I have talked with Fronius and it looks like they may send an IG+ as
> an upgrade. Perhaps the IG+ does not get confused by meter reading
> signals. Fingers crossed. If it does go into state 104 maybe opening
> up the frequency window will help.
>
> We have no other inverters on this utility for comparison and have had
> no feedback on the hand full of grid-tied systems out there.
>
> Thanks for the valuable input,
>
> Jeff
>
>
> Jeff Wongstrom
> NABCEP Certified
> 406.291.3416
> thirstylakesolar.com <http://www.thirstylakesolar.com>
>
>
>
> On Oct 8, 2012, at 7:38 PM, Kent Osterberg wrote:
>
>> Jeff,
>>
>> Is there any chance the utility has recently implemented a remote
>> meter reading system? The Aclara TWACs
>> <http://www.aclaratech.com/AclaraPLS/specsheets/TWACS_UMT-R.pdf>
>> remote meter reading system communicates by putting a pulse on the
>> line that is very near the zero crossing of the voltage waveform.
>> Unfortunately the zero crossing is easily and often used as a
>> reference point for frequency measurements. Devices that watch the
>> zero crossings are often confused by the TWACS signal. The signal
>> isn't there constantly -- only when the local kWr meter has been
>> asked to send data.
>> Kent Osterberg
>> Blue Mountain Solar, Inc.
>> www.bluemountainsolar.com
>> t: 541-568-4882
>> On 10/8/2012 9:34 AM, Jeff Wongstrom wrote:
>>> Hello wrenches,
>>>
>>> We have a Fronius IG3000 that chronically and frequently cycles into
>>> and out of a state 104(grid frequency not within admissible range).
>>> The utility has monitored the supply and claims to have found no
>>> frequency or supply issues. Fronius sent a replacement inverter
>>> but the error persists. The tie in point was moved from the critical
>>> loads sub panel to the main distribution panel. The state 104
>>> persists with ALL other breakers open. A Fluke DMM min/max function
>>> captures no frequency readings outside of the inverter frequency
>>> window-same with voltage readings.
>>>
>>> Any suggestions or recommendations?
>>>
>>> Thanks,
>>>
>>> Jeff
>>>
>
>
>
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5317 - Release Date: 10/08/12
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121009/86ccb60b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5311 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121009/86ccb60b/attachment.jpeg>
More information about the RE-wrenches
mailing list