[RE-wrenches] Fronius State 104
Kent Osterberg
kent at coveoregon.com
Mon Oct 8 18:38:11 PDT 2012
Jeff,
Is there any chance the utility has recently implemented a remote meter
reading system? The Aclara TWACs
<http://www.aclaratech.com/AclaraPLS/specsheets/TWACS_UMT-R.pdf> remote
meter reading system communicates by putting a pulse on the line that is
very near the zero crossing of the voltage waveform. Unfortunately the
zero crossing is easily and often used as a reference point for
frequency measurements. Devices that watch the zero crossings are often
confused by the TWACS signal. The signal isn't there constantly -- only
when the local kWr meter has been asked to send data.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882
On 10/8/2012 9:34 AM, Jeff Wongstrom wrote:
> Hello wrenches,
>
> We have a Fronius IG3000 that chronically and frequently cycles into
> and out of a state 104(grid frequency not within admissible range).
> The utility has monitored the supply and claims to have found no
> frequency or supply issues. Fronius sent a replacement inverter but
> the error persists. The tie in point was moved from the critical loads
> sub panel to the main distribution panel. The state 104 persists with
> ALL other breakers open. A Fluke DMM min/max function captures no
> frequency readings outside of the inverter frequency window-same with
> voltage readings.
>
> Any suggestions or recommendations?
>
> Thanks,
>
> Jeff
>
>
> Jeff Wongstrom
> NABCEP Certified
> 406.291.3416
> thirstylakesolar.com <http://www.thirstylakesolar.com>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121008/57c79178/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5311 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121008/57c79178/attachment.jpeg>
More information about the RE-wrenches
mailing list