[RE-wrenches] Outback with grid charging
toddcory at finestplanet.com
toddcory at finestplanet.com
Fri Aug 24 10:40:35 PDT 2012
i am not understanding the 'wisdom' of using non-grid tie inverters in this application. it is pretty easy to modify the inverters (board change out) to grid tie models, which would allow the inverter's to transfer the loads to the grid (internal transfer switch) and 'sleep' until there is an outage to back up. the only additional use the system would bring to their bill is re-floating the batteries occasionally.
with no renewable input (except silly, yard-art wind gennys), basically they have an expensive whole-house ups. i wonder what the intention or original design was supposed to do?
todd
On Friday, August 24, 2012 9:14am, "Jesse Dahl" <dahlsolar at gmail.com> said:
I do not want to take this on! The wind, from what I have gathered is an absolute bust. Just doing a little online research it seems like they are getting next to nothing from the wind generators.
From my little understanding of the system and reading replies, I would say they are buying power, losing 30% of it and then powering loads.
This system was installed by a contractor in Duluth, MN.
Jesse
Sent from my iPhone
On Aug 24, 2012, at 10:31 AM, Kent Osterberg <[mailto:kent at coveoregon.com] kent at coveoregon.com> wrote:
Two 1-kW wind generators doesn't sound like enough to provide energy for a household except possibly in the best circumstances. If there isn't much wind, the system is getting most of it's energy from the grid. The utility bill would go up even if they were using the same amount of energy in the house. Batteries are energy losers!
What Dave and others have warned about kWh metering issues is also true. The new digital meters have many capabilities and the default for most of them is to record energy going in either direction as energy consumed. Since they are programmable, the same meter can be used to record net energy - behave like most disk-type meters; ignore energy in one direction - behave like a detented meter; or record both incoming energy and outgoing energy separately - a two register meter.
Kent OsterbergBlue Mountain Solar, Inc.[http://www.bluemountainsolar.com] www.bluemountainsolar.comOn 8/24/2012 6:26 AM, Jesse Dahl wrote:
The system only uses grid power to charge batteries, they have two FX3048T in parallel so I don't think the meter is the issue.
They did send me a picture of the two wind towers, one is 20 feet off the ground and one is 60 feet off the ground... No wind would be an understatement.
Sent from my iPhone
On Aug 24, 2012, at 7:43 AM, David Katz <[mailto:dkatz at aeesolar.com] dkatz at aeesolar.com> wrote:
Check to see if their meter goes backwards. Some utility meters actually charge for power when you are selling.
Or maybe they have no wind and a new big flat screen tv that they leave on all the time.
David Katz
----- Reply message -----
From: "Jesse Dahl" <[mailto:dahlsolar at gmail.com] dahlsolar at gmail.com>
To: "Wrenches" <[mailto:RE-wrenches at lists.re-wrenches.org] RE-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Outback with grid charging
Date: Thu, Aug 23, 2012 11:28 pm
Hello,
I got a call from a family today about a system they had installed recently and they think they have a problem. They claim their electric bill has just about doubled since the system has been installed due to outback using the grid to power the loads instead of the battery bank. They claim the MATE always shows the system buying the exact amount as any load on the system draws. Due to the distance from my shop, I would like to get any ideas on what could cause this before I drive all the way there.
What I know about the system:
2 - outback inverters, 48v
2 - whisper 500 wind generators with whisper charge controllers
16 - MK 12v AGMS (8/inverter)
I guessing setting, but if anyone has seen this before, I'd like to narrow it down before the drive.
Thanks eh!
Jesse
Sent from my iPad!!!
_______________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: [mailto:RE-wrenches at lists.re-wrenches.org] RE-wrenches at lists.re-wrenches.org
Options & settings:
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: [http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
[http://www.re-wrenches.org/etiquette.htm] www.re-wrenches.org/etiquette.htm
Check out participant bios:
[http://www.members.re-wrenches.org] www.members.re-wrenches.org
Sent from Finest Planet WebMail.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120824/f3811355/attachment.htm>
More information about the RE-wrenches
mailing list