[RE-wrenches] Critical Loads Panel Wiring

Darryl Thayer daryl_solar at yahoo.com
Tue May 8 06:42:33 PDT 2012


Locally if you have two service panels next to each other, inspectors want both bonded and grounded, by allowing a bonding jumper from panel one to panel 2, and both panesl use the bonding screw, and both have to have a neutral bus.  

 

________________________________
 From: Corey Shalanski <cshalanski at joule-energy.com>
To: RE-wrenches at lists.re-wrenches.org 
Sent: Tuesday, May 8, 2012 6:51 AM
Subject: [RE-wrenches] Critical Loads Panel Wiring
  

Wrenches,

Batt backup system: When placing a critical loads panel directly adjacent to the main service panel (in the next stud bay), must the neutral and ground conductors be pulled into the new subpanel? or can only the hots be pulled? Any Code references would be appreciated. 

--
Corey Shalanski
Joule Energy
New Orleans, LA 
_______________________________________________
List sponsored by Home Power magazine