[RE-wrenches] Off-Grid to Grid-Connected -essential loads
William Miller
william at millersolar.com
Sun May 6 11:02:41 PDT 2012
Colleagues:
I might caution against using the HBX mode for two reasons:
1. The batteries will "wear out" in proportion to the number of cycles. If
you don't need to cycle then I recommend you don't.
2. HBX can be a very inefficient mode. If you HBX cycle frequently then
you are double-converting your power: Converting AC to DC to charge
batteries and then converting DC to AC to power loads.
William Miller
At 08:43 PM 5/4/2012, david at wind-sun.com wrote:
>Eventually all batteries wear out but that is no reason to give up on them
>because the grid is coming in. It sounds like he simply wants to continue
>using his off-grid system and let the grid take over if the modules can't
>keep up with the demand. If you're using outback inverters simply program
>them for HBX mode.
>
>
>David Lauzon
>Northern Arizona Wind and Sun Phone-928-526-8017 / 800-383-0195
>Fax-928-527-0729
>Website-<http://www.solar-electric.com>http://www.solar-electric.com